How is that working for you? I have a 130 model which closes the bypass at 148.My boiler protection is set at 115* which fully closes the bypass at 133* so I can heat up my storage quicker.
No complaints. As long as the boiler is protected it just makes sense to start putting the extra 15* into storage. It only comes into play at the start of the heating season and after a mid season cleaning because I never let my boiler temp get that low. Although with the price of oil Im starting to think about using that. Do you run your oil much?How is that working for you? I have a 130 model which closes the bypass at 148.
I only run the pellet boiler when I'm 'experimenting', but I've been 'experimenting' a lot.Do you run your oil much?
I tried setting the external boiler temp to 147, with the boiler set temp at 176. A couple zones running, 66 & 68, about freezing outside.
It ran for 5hours 45minutes and then shut itself off at a boiler temp of 170.
I wonder if there is a duration that the boiler can run before it shuts itself down?
It is a latched relay connected to the buffer aquastat. The boiler runs until the boiler shuts itself off.What exactly is your external demand connected to on the Windhager?
That explains it! What happens then is that the buffer tank supplies the load until the aquastat is triggered again.All BioWins automatically cycle off for a brief cool down/cleaning period every 6 hours of run time.
Heaterman, 1) what lengths should be pursued to increase run time? and 2) is it possible to connect to the BioWin with a 0-10volt controller to control boiler temperature (external)?
With the boiler external temp set at 170, things were more vigorous. I just saw 190 on the display only it was after the boiler shut itself off. It shut itself off at 181, the pumps runs as it always does for about 13 minutes, and then after it sat a little while, it rose to 190. Maybe I should arrange for a longer run, but that would take more finagling.its has gone up to as much as 189 on the Biowin display but has never shut itself off.
I have a sensor for a Ranco controller 1/3 from the top of the tank. When it goes down to 130F, a relay closes which remains closed until the boiler turns itself off at 181 or so. After the boiler turns itself off, the relay is unlatched and is free to close again when the temperature goes down again in the tank. It's connected to the terminals on the Windhager that turn the thing on an off.
Would you be able to tackle those other questions I had: 1) what lengths should be pursued to increase run time? and 2) is it possible to connect to the BioWin with a 0-10volt controller to control boiler temperature (external)?
When the one sensor on the tank senses that the temperature the tank at a point 1/3 from the top is below 130, the boiler starts. The boiler continues to run until it turns itself off, usually at 179 or so. The sensor's controller is then released to turn on the boiler again when the temperature is below 130. That's what I mean when I say it is latched. I did it that way because I wanted maximum, consistent fill of the buffer tank.So the relay opens based on boiler temp instead of storage temp? If so, why? I mean how can that be?.......... does it have a sensor in the storage tank and on or in the boiler piping?
Ah hah. That's good info. Now to figure out what to set it at. I'll try to make those charts look a little better tomorrow.Running at 30-40% for extended periods (over half the burn cycle) is not the greatest for efficiency.
Yes, it was running a bunch at low firing rate. That was with some load, not just the tank. I made a chart of one, but I kind of lost it towards then end. I'm logging this manually!If your boiler is running for the 6 hour maximum run time I'd bet that it's spending a good part of that at greatly reduced firing rate unless it is matched very closely with your actual heat loss.
My only concern is am I putting undo wear on the boiler's (unreplaceable) relay or whatever that turns things off? I mean, there are plenty of other electrical doo-dads in the boiler that can go south, right? It operates maybe 4 times a day, or whatever.
Rather than a 0-10Vdc control, you'd be farther ahead letting a Tekmar outdoor rest control manage the water temp in your storage.
Simply connect the output leads from it to the xx connections on your Windhager board and watch what happens. Set minimum water temp at 125 - 130 on the Tekmar.
Who said there was a problem? I'm obsessive.