You did a good job on figuring this out, rather safe than having the prv start to leak. The total expansion volume is what will change most once it hits 185f as you see on your calcs.Thanks for the feedback. I'm a little concerned at this point but not ready to order another tank yet. My wallet is still scorched from the recent flurry of orders ;-)
The Watts calculator run for 12psi - 28psi, 40F - 190F and 850 gal said the required acceptance was 26.6 gal. The two tanks on order will provide 42.6 gal which seems like about 60% more than required but this turns out to not be relevant (more below). The overall required tank volume of 105.4 gal is the limiting factor and the tanks will provide 106 gal which is very close at 28psi max.
The actual system volume will be closer to 825 gal and it will probably only be run to 185F so there's a little extra safety margin there. Also, only the storage and boiler loop will be at the max temperature. All the radiant loops will only be around 105F max and the radiators 140F max. There is very little volume in the water heater preheat loop. This will reduce the effective system volume to around 810 gal.
The initial fill pressure could also be reduced a little since the maximum height in the system is only 12'. The minimum pressure for 12' should be (elevation in feet / 2.31 feet per psi) + 4psi = 9.2psi, or rounded up to 10psi. The max pressure can then be reduced to 25psi as you suggested.
Re-running the calculator for those conditions, 10psi - 25psi, 40F - 185F and 810 gal, drops the required acceptance from 26.6 gal to 23.8 gal and the required tank volume from 105.4 gal to 91.1 gal which is a much more comfortable margin.
This whole expansion tank business was still a bit confusing to me. Digging deeper and using the Watts tool to generate a plot of max pressure vs. acceptance volume for a fixed expansion tank total volume of 106 gal, 40F - 190F, 12psi min was helpful. It turns out that the tanks on order will only accept 42.6 gal once the pressure reaches about 40psi, far above the 30psi PRV limit. I also ran the numbers for a 106 gal expansion tank, 40F - 185F, 10psi min for comparison. Both with 825 gal water total.
View attachment 330431
With the ability to make these changes if needed, it seems like the tanks on order should work OK. If necessary, another smaller tank can be added later. I'll add another tee and cap it off just in case.