CJS said:so are these the "integral ball valves" that are being referred to here?
...
Thanks for the tip free75... sounds like things got a little hot for you! I'm glad you had a happy ending so to speak. So by opening and closing those integral valves you think you freed something up and got it working better? I'm certainly wiling to give those a few twists back an forth. My tank is still at 155F today and the suns out so I may not fire again until we need some heat... but I'll give this a try and report back in the next couple of days after I fire it up again.
Yes those are what I am talking about and they all appear to be in the open position in your photo. As soon as I toggled those valves the boiler temp dropped rapidly after having been railed near 100*C. I think the termovar might have been stuck on all hot and toggling the valves got some cold to be included, so the heat was all of a sudden being dumped into the tank as it should have been doing all along. I am going to test it again tonight...
I know you have the bypass, but it still might be possible that your termovar is stuck on "all hot" and this is causing you problem. If it is stuck on all hot then the circ can basically pull from either the all hot termovar or the tank via the bypass. If the tank HX has more head loss than than the all hot temovar (which it probably does) then the bypass won't really be doing much - the termovar would supply almost all of the return water to the boiler due to the lower head loss.