First, thanks to everyone for a great forum. I've learned a tremendous amount here- and hope someone might be able to point me in the direction of a solution for my current situation.
I've got a Tarm Solo Plus 60 set up with storage in the form of a 1,000 gallon dairy tank to heat the radiant slab of our small business. A local plumber set it up with the help of the good folks from Tarm in NH. This project has been a learning experience for our plumber who has maintained a good attitude through the project. We are having some issues at the moment and while I'm definitely not a plumber/engineer, I'm trying to help brainstorm and ask the right questions that might point him to the bottle neck.
Basically, our situation is this. I fire up the Tarm, the water jacket comes up to 140F and the circulators come on moving water jacket water through a heat exchanger which transfers it to the loop that takes the hot water into the storage tank's copper loop exchangers. Within 45 minutes to an hour the temperature of the Tarm water jacket reaches its upper limit and turns off the fan, stopping combustion. Slowly the water jacket temp drops as the pumps and exchangers do their thing, the fan kicks back on and burns again for a number of minutes before maxing out and turning off again.
This is a new system installed this spring. We did a test fire this summer with the plumber and a rep from Tarm USA there to hold our hands. We had the same issue then. Rene from Tarm hypothesized that since our storage tank temperature was only 68F the Termovar valve was not allowing much tank water to be pulled in and heated, so the Tarm quickly reached the temperature for fan shut-off. To alleviate this situation during the annual start up (we have limited DHW needs and decided to not heat the tank year round) the plumber installed a bypass to the Termovar to bring the tank water up to temp more quickly, and once in normal operating range we'd shut down the by-pass (perhaps this is a no-no??)
Well now we are in the heating season and even with the by-pass open, the Tarm water jacket is quickly reaching 180F+ shutting off the fan and smoldering.
We were really looking forward to high-efficiency, wide-open burns to charge our tank and are frustrated with the creosote dripping out the bottom of the chimney and from around the upper door gasket.
The plumber is operating on the thought that air is trapped in the tank's heat exchanger coil loops and preventing good heat transfer. He assures me the pumps/pipes and the heat exchanger that separate the Tarm from everything else are sized as specified by the Tarm USA folks.
Has anyone had similar troubles bringing their tanks up to temp? Do other people's wood-gasification boilers cycle on and off when operating with storage? Short of reviewing the details of every valve and pump can anyone offer any general advice of things to check?
We've got the tank temp up to 140F today, but the fan/combustion is still cycling on and off.
Thanks to those of you who made it this far down- any thoughts are appreciated.
I've got a Tarm Solo Plus 60 set up with storage in the form of a 1,000 gallon dairy tank to heat the radiant slab of our small business. A local plumber set it up with the help of the good folks from Tarm in NH. This project has been a learning experience for our plumber who has maintained a good attitude through the project. We are having some issues at the moment and while I'm definitely not a plumber/engineer, I'm trying to help brainstorm and ask the right questions that might point him to the bottle neck.
Basically, our situation is this. I fire up the Tarm, the water jacket comes up to 140F and the circulators come on moving water jacket water through a heat exchanger which transfers it to the loop that takes the hot water into the storage tank's copper loop exchangers. Within 45 minutes to an hour the temperature of the Tarm water jacket reaches its upper limit and turns off the fan, stopping combustion. Slowly the water jacket temp drops as the pumps and exchangers do their thing, the fan kicks back on and burns again for a number of minutes before maxing out and turning off again.
This is a new system installed this spring. We did a test fire this summer with the plumber and a rep from Tarm USA there to hold our hands. We had the same issue then. Rene from Tarm hypothesized that since our storage tank temperature was only 68F the Termovar valve was not allowing much tank water to be pulled in and heated, so the Tarm quickly reached the temperature for fan shut-off. To alleviate this situation during the annual start up (we have limited DHW needs and decided to not heat the tank year round) the plumber installed a bypass to the Termovar to bring the tank water up to temp more quickly, and once in normal operating range we'd shut down the by-pass (perhaps this is a no-no??)
Well now we are in the heating season and even with the by-pass open, the Tarm water jacket is quickly reaching 180F+ shutting off the fan and smoldering.
We were really looking forward to high-efficiency, wide-open burns to charge our tank and are frustrated with the creosote dripping out the bottom of the chimney and from around the upper door gasket.
The plumber is operating on the thought that air is trapped in the tank's heat exchanger coil loops and preventing good heat transfer. He assures me the pumps/pipes and the heat exchanger that separate the Tarm from everything else are sized as specified by the Tarm USA folks.
Has anyone had similar troubles bringing their tanks up to temp? Do other people's wood-gasification boilers cycle on and off when operating with storage? Short of reviewing the details of every valve and pump can anyone offer any general advice of things to check?
We've got the tank temp up to 140F today, but the fan/combustion is still cycling on and off.
Thanks to those of you who made it this far down- any thoughts are appreciated.