What kind of filter(s) do you have in? If you go to a higher MERV filter that will lower the CFM output some too...
I just put in two filtrete filters, I believe they are 1500 MERV. I thought about increasing the MERV, and for the sake of throwing ideas around, I thought about the idea of stacking up filters to increase resistance but I can't imagine that being good for the blower. Choking the return side to address a supply line issue feels like cheating and masking the problem and I'm wondering if that may be bad for the blower? Not only that, but the high pressure is indicative of a low flowing system. If I do manage to substantially reduce my pressure I may be getting little to no flow of air coming out of my vents.
So supply duct is 160 sq inches (probably a bit on the small side) and then that goes into flex line?
Return line is 154 sq inches...which should actually be at least 10% bigger than the supply.
Correct, but since the supply line is being bottlenecked by the 6" flex ducts, I'm guessing this set up resembles a system where the return is 25-50% larger than the supply. If I replace some of the flex with rigid duct then I may get to a point where the return air needs to be addressed.