This is what I am thinking for my boiler piping- please take a look.
During heat storage, P1 and P2 are activated. V3 and V4 are open. V5and V6 are closed. P3 is activated for thermostat calls. The E180 acts as the heat source for both the house and for thermal storage.
Once the heat storage is full (probably according to a timer set by the user at the time of firing), All pumps are shut down, and the valve settings are reversed. V3 and 4 are closed, and V5 and V6 are open. Thermostat calls activate P1 and P3. The E180 acts as the heat source for the house only.
Once the E180 cools down (when it runs out of wood) V1 closed and P1 turns off. Thermostat calls activate P2 and P3. The thermal storage is the heat source for the house.
V2 is a boiler protection shunt that injects warm water into the boiler return to avoid thermal shock (set to 180F.)
The 4 valves around P2 act to reverse water flow in the thermal storage in order to change from storing heat to delivering heat to the house.
There is room for expansion on the far right- in case I need to heat a pole barn, hot tub, etc.
Thanks- I appreciate your input!
Andrew
During heat storage, P1 and P2 are activated. V3 and V4 are open. V5and V6 are closed. P3 is activated for thermostat calls. The E180 acts as the heat source for both the house and for thermal storage.
Once the heat storage is full (probably according to a timer set by the user at the time of firing), All pumps are shut down, and the valve settings are reversed. V3 and 4 are closed, and V5 and V6 are open. Thermostat calls activate P1 and P3. The E180 acts as the heat source for the house only.
Once the E180 cools down (when it runs out of wood) V1 closed and P1 turns off. Thermostat calls activate P2 and P3. The thermal storage is the heat source for the house.
V2 is a boiler protection shunt that injects warm water into the boiler return to avoid thermal shock (set to 180F.)
The 4 valves around P2 act to reverse water flow in the thermal storage in order to change from storing heat to delivering heat to the house.
There is room for expansion on the far right- in case I need to heat a pole barn, hot tub, etc.
Thanks- I appreciate your input!
Andrew