Or it’s defective? Can you get the static pressure in spec? If it is and it’s tripping off so then it’s a bad fan and should be replaced under warranty.
@EbS-P
Possibly. Let me explain how I'm measuring static in case there are any experts in here who see something wrong.
Ideally, I'd measure static as the sum of the pressure immediately before the coil (on the return side) and immediately after the fan (on the supply side). The manufacturer charts don't indicate if the measurements include a filter, so I've assumed they do not.
It's easy enough to measure the pressure after the fan (hole in the duct - blue tape spot in the picture I posted), but not immediately before the coil without drilling my HVAC cabinet (because the filter sits in that slot below the coil). So I have been taking the filter out, making the measurements (at a hole in the return box - another blue tape spot in the picture), and then estimating that a spun fiberglass filter adds about 0.1"WC to it.
If my measurement and assumption for filter pressure drop are good, the current operating speed has me 0.52" if both zones are calling, 0.58" if zone 1 is calling, and 0.65" if zone 2 is calling. This is with basement supply and return open.
If I close the return vent in the basement, the static pressure measures 0.6" with both zones open, 0.68" with zone 1 open, and 0.71" with zone 2 open.
With a rating of up to 1.0"WC, I would think it's in range in either case. The zone panel is designed to soft start, meaning it leaves zone dampers open when it's done to avoid having high pressure issues, so I don't think there are transient spikes I'm getting. I'm not running AC at this point in the year, so I'm certain the coil is not freezing up (even when it defrosts, it doesn't stay there long enough to ice the indoor coil).
The fan has not tripped so far when I leave the basement supply and return open. If I close the basement return, it has tripped 3-4 times. It may run for a month before it happens. The trip last night happened within the first day of having that return closed.
Could my measurements be off? Sure, I'm no pro, I'm guessing at the midpoint of a number that bounces around on the manometer, and the manometer I'm using is a cheap one off Amazon. Could I be underestimating the filter pressure drop? I guess that's possible too. I found 0.1" as a typical pressure drop of a spun fiberglass filter, but that could be evaluated at a lower flow rate. If it's 0.2" or 0.3" or more, then my actual static pressure might be out of range.
Incidentally, I measure power consumption of the indoor fan motor at about 500-525W. It is rated for 750W, I believe. I've not seen it spike that high at all.
The other possibility I've been considering is that the high temperature differentials I'm seeing (40+ degrees) might be overheating the motor. If the compressor is ramping up uncontrolled, it may be creating too much heat in the cabinet and causing the motor to trip. On the old system, I'd never see over 90 degrees leaving air temperature. With this system I regularly see over 90, sometimes as high as 108-109 degrees F. That's with no heat strips operating.