Hello.
I have all the instrumentation for the new Pacific Energy Summit LE Insert up and running. I have some initial readings from a fire today, just to see how things are woking. It is 50 degrees outside and no wind. With my prior installation my draft was very high (measured > 0.2) and contributed to the failure of my prior install.
My initial readings of draft after getting a ~3/4 loaded box up to a steady cruise, gas path temp at a steady 850ish degrees F about 7 inches up the flue, show that the draft still at 0.15, greater than the max recommended by Pacific Energy of 0.10. Metal temperature across the face just above the door in the 550 degrees F neighborhood.
The 0.15 in-col of water reading is with the air inlet FULLY CLOSED and the damper FULLY CLOSED.
I imagine with colder days and a full packed box the draft might increase even more.
Should I be concerned? I was really hoping to be able to drive the fire to a "stall" with the new damper, or at least down to within spec of 0.1 in-col of water. While this might be "better" in terms of control I am concerned. Those who warned the Pacific Energy Summit would also breathe easy were spot on.
Thoughts and opinions appreciated.
Additional thoughts/information:
1) It appears the air inlet really does not close as far as I'd like (see picture, she's alive). I've seen folks modify the inlet lever to close further. Any thoughts/opinions on this?
2)) There is a photo of my selected location for the Magnehelic. As far as DEPTH of the probe, the reading does not change from just inside the flue wall to the probe being 4" in, well behind the damper. As such I think I will be getting better and more accurate reading than I feared. I will switch to the surface mounted fitting for simplicity (won't need to remove probe for cleaning). I was worried the air velocity rushing around the damper near the flu wall would result in a skewed measurement. This is the NOT the case and will simplify the draft sensor install.
3) The remote temperature sensor is working 75' away and up one story in the home with no issues. Appreciate this recommendation from @bholler . You have eliminated my early trips downstairs to see what's going on with the fire.
I have all the instrumentation for the new Pacific Energy Summit LE Insert up and running. I have some initial readings from a fire today, just to see how things are woking. It is 50 degrees outside and no wind. With my prior installation my draft was very high (measured > 0.2) and contributed to the failure of my prior install.
My initial readings of draft after getting a ~3/4 loaded box up to a steady cruise, gas path temp at a steady 850ish degrees F about 7 inches up the flue, show that the draft still at 0.15, greater than the max recommended by Pacific Energy of 0.10. Metal temperature across the face just above the door in the 550 degrees F neighborhood.
The 0.15 in-col of water reading is with the air inlet FULLY CLOSED and the damper FULLY CLOSED.
I imagine with colder days and a full packed box the draft might increase even more.
Should I be concerned? I was really hoping to be able to drive the fire to a "stall" with the new damper, or at least down to within spec of 0.1 in-col of water. While this might be "better" in terms of control I am concerned. Those who warned the Pacific Energy Summit would also breathe easy were spot on.
Thoughts and opinions appreciated.
Additional thoughts/information:
1) It appears the air inlet really does not close as far as I'd like (see picture, she's alive). I've seen folks modify the inlet lever to close further. Any thoughts/opinions on this?
2)) There is a photo of my selected location for the Magnehelic. As far as DEPTH of the probe, the reading does not change from just inside the flue wall to the probe being 4" in, well behind the damper. As such I think I will be getting better and more accurate reading than I feared. I will switch to the surface mounted fitting for simplicity (won't need to remove probe for cleaning). I was worried the air velocity rushing around the damper near the flu wall would result in a skewed measurement. This is the NOT the case and will simplify the draft sensor install.
3) The remote temperature sensor is working 75' away and up one story in the home with no issues. Appreciate this recommendation from @bholler . You have eliminated my early trips downstairs to see what's going on with the fire.