Set up includes a Tarm Solo 60 with 1200 gallons of pressurized storage. Boiler/Storage circ is a 26-99 three speed set on medium. Off of the storage loop is a alpha 15-55 for DHW through a side arm exchanger and a water to air exchanger in the furnace plenum( both run off of zone valves off of the Alpha). The problem is that the alpha is usually pumping to the sidearm on the DHW heater. This is usually at approxiamately 13 gpm. When this is happening I'm not getting any flow through the tanks and the water is coming back to the termovar still hot.. Then the boiler will idle and I have 1200 gallons of water to heat yet. Do I need to do some repiping or can the return from the heat exchangers go back to the middle port on the tank. Then the water going back to the termovar would come directly from the bottom of the tanks? I couldnt figure out why it takes so long to charge the tanks until I just unplugged the Alpha. HOLY COW ,INSTANT TANK HEAT. Go to https://www.hearth.com/talk/threads/66701/ for plumbing schematic.