It sure seems to me that the house zone is pulling water from the Taco Mixing Valve, going around the boiler. That's the only way I see how the cast iron suction feeding the house zone pump is cold while the boiler high temp is kicking on.
I think people missed the note about the T's and are taking the drawing to mean 4 connections to the boiler. The mixing valve is drawn odd too, is this the actual valve orientation in the install? I would expect the mixed leg discharging into the radiant load in the garage.
I would be nervous having my near-boiler piping in pex like that, would feel much better with copper or black iron. And not 100% sure from the pic, but that looks like the kind of underground piping that might end up sending a lot of your heat into the ground eventually - are both lines together in the same cavity?
Is this a pressurized boiler/system?
Can you post a pic of the side arm?
What is the cord hanging down in pic #4, that's not for the circulator is it?
Here's the tell on your installation....."Plumber does not necessarily mean knowledgeable in boilers."
karl
In the picture I have the valve above the tank shut so that I'm not cooling the water in the tank. The pump was circulating cool water.
This is a unique situation for this model of boiler that doesn't happen to other manufacturers that have the supply at the top and the return at the bottom.
Speaking to a troubleshooting rep for Heatmaster, the G200 is very sensitive to supply/return flow rates. Apparently there are baffles and manifolds inside the boiler that direct cold water to certain places. If the flows are not at least 14 GPM there is a stratification issue inside the boiler and the supply water will never get hot while the top of the boiler will boil over. Having low flow and a high delta T like this scenario is, it will only exacerbate the problem as the cold water will fall to the bottom of the boiler and cause extreme stratification.
Based on what you're saying there is a problem with stagnant areas in the heat exchanger boiling while cold water bypasses that area despite the baffles/manifolds fix they tried? Their graphic of the inside of their boiler looks like a conventional fire tube hx although the sump area of the tank is pretty tight. Stratifying isn't the right word to use but I see what you mean.
Speaking to a troubleshooting rep for Heatmaster, the G200 is very sensitive to supply/return flow rates. Apparently there are baffles and manifolds inside the boiler that direct cold water to certain places. If the flows are not at least 14 GPM there is a stratification issue inside the boiler and the supply water will never get hot while the top of the boiler will boil over. Having low flow and a high delta T like this scenario is, it will only exacerbate the problem as the cold water will fall to the bottom of the boiler and cause extreme stratification.
In typical boiler designs with storage stratification is your friend, but in this model of boiler the supply and return are located closer together in the middle of the water jacket. This is a unique situation for this model of boiler that doesn't happen to other manufacturers that have the supply at the top and the return at the bottom.
To resolve the issue he needs to get the flow rates up with a secondary mixing pump, or make some plumbing adjustments and add another pump for higher flow rates.
In going through two pages of answers, the simple answer is that you still have inadequate flow in the system. If the boiler requires 14gpm, I think I can guarantee that there is no way this system as plumbed will ever do that.
This system would greatly benefit from a primary/secondary plumbing design, separating the garage from the house, putting them both in parallel.
A flow meter or two would be appropriate as well.
I am thinking that if a boiler requires that much flow through it when burning (and it sounds like the case here), it should have and come with a pumped bypass loop to ensure it. I don't have great exposure to a lot of systems - but 14gpm is sounding kind of on the high side for system flow, and more often than not a typical system won't flow that much. I could be wrong on that, but mine flows less than 10. What would a typical range of system flows be?