Jim K in PA said:Interesting. I would think that with Steve's customer's high-flow setup that there would be enough mixing to disturb that pocket of warm water up at the front wall temp gauge. Apparently not! That front bung is about as far away from the return bung as you can get.
Jim - your project with the 3200 - keep in mind that like any storage system, you are NOT going to have a constant supply temp like you would have in a constant firing appliance like an oil or gas furnace. You can set up a mixing valve to reduce output temp to something below the max temp, but that only works until your tank drops below that point.
I think the lesson here is that no matter what piping arrangement you have, circulator controls should be based on temps in the PIPING, not on what the temps are at the front gauge or in a well attached to the tank. I have a temp well installed in the second bung on my WHS2000, but I only use that for remote temperature display. I have Tees with temp wells installed in the primary piping for (as yet unused) control circuits.
I thought it would upset the apple cart a bit also Jim. That 1400 is moving some serious GPM through the system and the thermocline in the Garn seems oblivious to it as the temp readings from bottom to top showed. I was really surprised that more blending wasn"t taking place.
I'll ditto the comment regarding the control setup and system being designed to work with variable water temps coming from any type of storage. That's why the method of heat transfer is just as important as the unit supplying the heat. The lower a person can use the better.