Unwanted or ghost flow can have multiple causes. Hot goes to cold always, so if there is a clear, low pressure drop piping circuit without any check or flow protection you will get energy transfer. This is how the old buildings heated with gravity hot water systems. Hot water would rise up the large diameter piping, cold would fall.
That transfer is so powerful that tall buildings needed balancing valves on the upper floors to prevent over heating and force some flow to the lower floors. That is one of the functions of those big wheeled valves on cast iron radiators in old gravity systems.
The taller that thermocline, the faster the hot would rise up.
Another cause of un-wanted flow is caused by circulator pumps moving flow to the path of least resistance. That is where check valves or flow control valves come into play. In some cases you may need check protection on both supply and return piping. Indirect tanks are a classic example of the need for checks on both sides.
It is hard to predict how and when ghost flows are going to haunt you. Vertical piping runs encourage it, cold tanks can also. You can even experience two direction flow in a pipe, hot water rising up the center, cold falling down around it.
Best to just design the piping components with flow protection at the get go. Pumps now have check protection built in or in the box with the pump, that solves one side. Add a spring "hydronic" check on the other side of the loop.
That transfer is so powerful that tall buildings needed balancing valves on the upper floors to prevent over heating and force some flow to the lower floors. That is one of the functions of those big wheeled valves on cast iron radiators in old gravity systems.
The taller that thermocline, the faster the hot would rise up.
Another cause of un-wanted flow is caused by circulator pumps moving flow to the path of least resistance. That is where check valves or flow control valves come into play. In some cases you may need check protection on both supply and return piping. Indirect tanks are a classic example of the need for checks on both sides.
It is hard to predict how and when ghost flows are going to haunt you. Vertical piping runs encourage it, cold tanks can also. You can even experience two direction flow in a pipe, hot water rising up the center, cold falling down around it.
Best to just design the piping components with flow protection at the get go. Pumps now have check protection built in or in the box with the pump, that solves one side. Add a spring "hydronic" check on the other side of the loop.