PassionForFire&Water
Minister of Fire
Try this link: (broken link removed to http://www.epa.gov/burnwise/pdfs/owhhphase2agreement.pdf)
Question: I need to think this through more, but what might be the reasons for the variation in efficiency calculation? Shouldn’t the 6050 btu/lb account for the difference between a dry weight calculation and a 20% MC calculation?
Frozen Canuck: It takes more energy to heat water from 150 -190 than it does to heat it from 110 - 150. Same 40 delta, so what’s up with this?
Frozen Canuck: It takes more energy to heat water from 150 -190 than it does to heat it from 110 - 150. Same 40 delta, so what’s up with this?
I need help with this one. If 1 btu will raise 1 lb of water 1F, then the same btu’s are required to raise a set volume of water from 110-150 as 150-190. So why more energy? You must have something else in mind in addition to energy required to raise the temperature of the water.
jebatty said:Garn deserves credit for posting the test report on the 1500; hopefully it will do the same for the 2000. And I hope other boiler mfrs post similar information, in detail. This kind of information will help shed light on many of the things that we discuss on the forum.
DaveBP said:Frozen Canuck: It takes more energy to heat water from 150 -190 than it does to heat it from 110 - 150. Same 40 delta, so what’s up with this?
I need help with this one. If 1 btu will raise 1 lb of water 1F, then the same btu’s are required to raise a set volume of water from 110-150 as 150-190. So why more energy? You must have something else in mind in addition to energy required to raise the temperature of the water.
It's not that it takes more BTUs to heat the water at the higher temp range but it's harder to get the water to absorb the heat since the deltaT , as Marc says, is lower between the flue gases and the water. It takes more heat to raise the temperature of the water but some of that extra energy is going up the flue, not into the water.
The amount of heat it takes to raise the temperature of water does vary with the temperature of the water, but I believe it's less that 1% over the range that wood boilers intentionally use.
heaterman said:DaveBP said:Frozen Canuck: It takes more energy to heat water from 150 -190 than it does to heat it from 110 - 150. Same 40 delta, so what’s up with this?
I need help with this one. If 1 btu will raise 1 lb of water 1F, then the same btu’s are required to raise a set volume of water from 110-150 as 150-190. So why more energy? You must have something else in mind in addition to energy required to raise the temperature of the water.
It's not that it takes more BTUs to heat the water at the higher temp range but it's harder to get the water to absorb the heat since the deltaT , as Marc says, is lower between the flue gases and the water. It takes more heat to raise the temperature of the water but some of that extra energy is going up the flue, not into the water.
The amount of heat it takes to raise the temperature of water does vary with the temperature of the water, but I believe it's less that 1% over the range that wood boilers intentionally use.
Viessmann told us at a training school that the real benefit comes when the water temp is low enough to get the flue gas into condensing territory which is generally below 140*. As such, there is not a lot of benefit unless you have a boiler that will tolerate water temps that low. I'm not aware of any standard gassers that are recommended to operate at <150*. I have seen many Garns however that are routinely operated down to the 110-120* range before firing. The Testo will tickle 90% at those temps. Once water temp gets up to 150+ the same unit will read 80-85%.
goosegunner said:heaterman said:DaveBP said:Frozen Canuck: It takes more energy to heat water from 150 -190 than it does to heat it from 110 - 150. Same 40 delta, so what’s up with this?
I need help with this one. If 1 btu will raise 1 lb of water 1F, then the same btu’s are required to raise a set volume of water from 110-150 as 150-190. So why more energy? You must have something else in mind in addition to energy required to raise the temperature of the water.
It's not that it takes more BTUs to heat the water at the higher temp range but it's harder to get the water to absorb the heat since the deltaT , as Marc says, is lower between the flue gases and the water. It takes more heat to raise the temperature of the water but some of that extra energy is going up the flue, not into the water.
The amount of heat it takes to raise the temperature of water does vary with the temperature of the water, but I believe it's less that 1% over the range that wood boilers intentionally use.
Viessmann told us at a training school that the real benefit comes when the water temp is low enough to get the flue gas into condensing territory which is generally below 140*. As such, there is not a lot of benefit unless you have a boiler that will tolerate water temps that low. I'm not aware of any standard gassers that are recommended to operate at <150*. I have seen many Garns however that are routinely operated down to the 110-120* range before firing. The Testo will tickle 90% at those temps. Once water temp gets up to 150+ the same unit will read 80-85%.
Heaterman,
With your experience with the Garn how does it perform when pushing it to higher temps for high temp emitters?
Many people here are under the impression that the Garn is not the best if using with forced air coil. Does that hold true in real world installs?
I am comfortably running my Econoburn with 1000 gallons of pressurized storage from 185 down to 140. My guess would be that the Garn with 1500 gallons would be even better if it would charge to 185 easily and say stratified.
One thing I don't understand is when the Garn users talk about the mixing pump, what is its purpose? Would that effect stratification for forced air system?
gg
heaterman: I’m not aware of any standard gassers that are recommended to operate at <150*. I have seen many Garns however that are routinely operated down to the 110-120* range before firing.
jebatty said:heaterman: I’m not aware of any standard gassers that are recommended to operate at <150*. I have seen many Garns however that are routinely operated down to the 110-120* range before firing.
Once again, I'm missing something. With the Garn hx tube snaking through the water, it seems to me that if [flue gas] is down to the 110-120F range, it will cool any water in the Garn that is higher than that temperature. Isn't that one of the chief reasons Garn is marketing a control that shuts the draft blower down as the fire burns down? And in the Garn 1500 test report, it is carefully mentioned that the fire is considered "out" when it no longer is raising the temperature of the water. That makes sense, otherwise the flue is cooling the water down. I will need it explained to me how flue gas lower than the temperature of the surrounding water works in the Garn to extract more heat from the near dead to dead fire.
I have seen many Garns however that are routinely operated down to the 110-120* range before firing.
heaterman: I’m not aware of any standard gassers that are recommended to operate at <150*.
jebatty said:It helps a lot, but I still need some clarity. First, I think I misunderstood your statement
I have seen many Garns however that are routinely operated down to the 110-120* range before firing.
I mistakenly took that to mean that Garns regularly operated with flue gas in the 110-120* range, and now I see that you meant that Garn water storage is regularly drawn down to this range before the Garn is refired. We all know that flue gas must be considerably above 212F to prevent condensation, and the Garn is no different in this regard than other gasification boilers.
I also now understand the new controller better. If on firing Garn water storage temp is brought up to 180F, for example, and as the fire burns down flue gas and air being drawn through the extraction tube drops to below 185F, the draft blower shuts down. Obviously there is no fire and no heat to be extracted to the water if flue gas is below 185F. This is a welcome addition to the Garn and would be very useful to all of the Garn owners who still rely on a timer that on occasion they may have set too long and the blower kept moving cold air through the Garn and cooling it down after the fire has burned out. The Tarm which I bought in 2007 was equipped with this kind of control and it too shuts the draft fan down when the flue gas has insufficient temp to add heat to the water.
Here is where I need more clarity because I think this statement is very misleading:
heaterman: I’m not aware of any standard gassers that are recommended to operate at <150*.
On a personal level I always operate my Tarm when storage temperature is less than 150*, and frequently down to 100*, as my radiant is supplied at 100* with a mixing valve. The Garn has integral storage, I have added storage with a 1000 gal tank I bought for $900. It is misleading to compare a gasification boiler without storage to a gasification boiler with storage, be that a Tarm with storage or a Garn with storage. You, me and others have consistently recommended storage for gasification boilers, as have manufacturers. I think on reflection you would agree that you are aware of a great many standard gassers with storage, and perhaps every gasser with storage that you are aware of, that are perfectly suited to operate when storage is < 150*.
goosegunner: Heaterman, With your experience with the Garn how does it perform when pushing it to higher temps for high temp emitters?
Many people here are under the impression that the Garn is not the best if using with forced air coil. Does that hold true in real world installs?
I am comfortably running my Econoburn with 1000 gallons of pressurized storage from 185 down to 140. My guess would be that the Garn with 1500 gallons would be even better if it would charge to 185 easily and say stratified.
Heaterman: The limiting factor is not the Garn but rather the hot water coil used in the furnace plenum.... A person should always install the largest heating coil possible in order to gain good response time (furnace blower not running endlessly) and maximum use of the water available before having to refire or reburn.
Maximum flexibility in your required water temperature is the goal because that is what allows long and sustained burns, which more than any other factor, make for clean and efficient combustion. Storage doesn’t do any good if your system demands 180* water under all circumstances.
jebatty said:goosegunner: Heaterman, With your experience with the Garn how does it perform when pushing it to higher temps for high temp emitters?
Many people here are under the impression that the Garn is not the best if using with forced air coil. Does that hold true in real world installs?
I am comfortably running my Econoburn with 1000 gallons of pressurized storage from 185 down to 140. My guess would be that the Garn with 1500 gallons would be even better if it would charge to 185 easily and say stratified.
Heaterman: The limiting factor is not the Garn but rather the hot water coil used in the furnace plenum.... A person should always install the largest heating coil possible in order to gain good response time (furnace blower not running endlessly) and maximum use of the water available before having to refire or reburn.
Maximum flexibility in your required water temperature is the goal because that is what allows long and sustained burns, which more than any other factor, make for clean and efficient combustion. Storage doesn’t do any good if your system demands 180* water under all circumstances.
This is partially true. Given that a system has installed the largest heating coil possible, then an ability to supply hotter rather than cooler water adds "Maximum flexibility in your required water temperature." For example, if a system requires 140* water and storage of a set volume can only deliver 175* water, that system will have less flexibility than if storage can deliver 185* water. In goosegunner's case, he has pressurized storage. A Garn has open storage, and if used in a pressurized system must employ a heat exchanger. Most heat exchangers are spec'd with a 10* approach temperature, meaning that if the open storage is at 185*, pressurized supply through the heat exchanger will be 175*. That is a loss of 10F in flexibility, or a loss of nearly 30% of usable storage capacity in this example.
Heat exchangers can be spec'd with closer approach temperatures, but the cost also rises dramatically. There is no feasible heat exchanger which can operate at 0F approach temperature to match the pressurized storage temperature. I work with a Garn system with a substantially oversized heat exchanger which achieves an approach temperature of 5* at 69 gpm, very good. But still, there is a loss of 5* in flexibility. For a 1500 gallon system, which is the smallest Garn that I know of, as compared to 1500 gallons of pressurized storage, that equates to a loss of 62,475 btu's at 5* approach and 124,950 btu's at 10* approach. Depending on heat demand, that can make a substantial difference. In my shop, with typical demand of 12,000 btuh, that is 5-10 hours of extra heat from pressurized storage as opposed to open storage and a heat exchanger.
heaterman said:If the boiler is allowed to "deal with" the full load of the storage under situations where it is much below the 140-150* level, a sticky mess will soon develop in the heat exchanger tubes.
The second thing that is different on a Garn is flue gas velocity which is much higher than any other unit I have seen.
Hope that clarifies things. It's as good as I can do with my limited knowledge.
hobbyheater said:heaterman said:If the boiler is allowed to "deal with" the full load of the storage under situations where it is much below the 140-150* level, a sticky mess will soon develop in the heat exchanger tubes.
The second thing that is different on a Garn is flue gas velocity which is much higher than any other unit I have seen.
Hope that clarifies things. It's as good as I can do with my limited knowledge.
A bit of history here. :bug:
The Jetstream regularly sees return water of 110F and I have never seen a sticky mess in the heat exchanger tubes. The cooler water inhibits the burning of wood in the loading tube.
Flue gas velocity is 1/3 the speed of sound through the refractory tunnel (nozzle).
Had the Garn been around in 1981, there would have likely been a Garn in our boiler room :exclaim:
goosegunner said:My system is pressurized because of the Econoburn with storage. I originally had a OWB with my forced air coil, it was not pressurized. If I had the Garn i would not have a heat exchanger between my load and the Garn water. I think that would allow the maximum use of the Garn storage.
The big question is how well does the Garn function when pushing the water to 185-190?
gg