It's a brand new air kit. Sealed good. They do have similar size houses. They have the blaze king model.Hmmm. not sure then, does everyone else have the same sq footage as you?
Is your oak attached well to the stove and not spilling that cold ext air into the room?
Not masonry, but veneer, inside wall.When you refill to the roof each time three times a day has the previous load burned down to nothing or are you just topping up a few splits above a big pile of coals?
3400 SF with masonry and 12 foot ceilings in a climate that is currently staying well below freezing is tough to keep warm and even tougher to warm up from 59.
Let's see a picture of "full load" running on high.But he says he's able to run a full load down in 6 hrs. At least he reloads in 6 hrs.
That doesn't suggest draft imo?
Red fir is a resinous fuel with anywhere from 8,500 to 9,500 btu's per lb. The 30.2 fire box can easily hold 45 lbs of fir. or using 9000 x 45 = 405,000 Btu's. 405,000/6 hours = 67,500 btu/hr Not possible in this stove. Even if it did generate that amount of heat, where is it going (especially with bypass closed).But he says he's able to run a full load down in 6 hrs. At least he reloads in 6 hrs.
That doesn't suggest draft imo?
I agree.Red fir is a resinous fuel with anywhere from 8,500 to 9,500 btu's per lb. The 30.2 fire box can easily hold 45 lbs of fir. or using 9000 x 45 = 405,000 Btu's. 405,000/6 hours = 67,500 btu/hr Not possible in this stove. Even if it did generate that amount of heat, where is it going (especially with bypass closed).
Internally, we always require pictures for tech support. Something is amiss here for certain.
BKVP