Another suggestion to increase flow would be to remove the strainer basket from this Y strainer. Even brand new, with a clean screen they have a few ft of pressure drop. With any crud in there it adds more pressure drop. Leave that basket in it for a day or two after any piping work to catch debris, then remove the strainer.
Always good to have isolation valves around components that will need service. One valve at each boiler connection and on the other side of the last component.
@heaterman oh trust me I've learned a huge amount of information I never thought existed. Anyone that talks about building their own boiler I cannot stress enough to them they need to do the research. I unfortunately did not when I started building mine. Which is why I'm here proving your fact 4 correct.
Very enlightening and comical, thanks for the laugh.Reading through this thread and thinking back over all the times I have seen this topic and others related to it discussed without end just makes my head hurt.
I should write a book or something to spare people the pain of doing things 5 times and still not understanding why it does not and will never work...
Here's a few bullet point comments regarding open systems, pumps and pipe size.
Fact 1
Open systems such as commonly found in factory built and home made wood burners present some issues that must be understood BEFORE attempting to pipe a system up.
Fact 2
These issues are related to simple laws of physics and if you try to cheat or circumvent them you will most definitely lose. EVERY TIME.
Fact 3
Many of these issues stem from undersized pipe/tube and oversizing pumps to try and compensate for the same.
Fact 4
There is never time or money to do it right the first time. There will ALWAYS be money and time to do it over.
Fact 5
Open systems have issues not present in a pressurized (real boiler) system which will cause you to learn more than you ever thought existed about piping and pumping
There are 2 basic solutions.
*Seal the system and pressurize it...which opens another can of worms... but hey, your pumps wouldn't cavitate.
*At a very elementary level... Double the size of tube you think you need and cut the size of the pump in half.
You'll spend more on tube, less on replacement pumps and your system will work.
Very enlightening and comical, thanks for the laugh.
Warno, I didn't bail on you. I m in the works of installing my own boiler and the whole family decided to get sick yesterday. I will be back.
There is only one data point, Im just not certain head loss is proportional to flow. It may be, I'd have to research a little. Even if not it's probably close enough for what we are dealing with.Isn't there a way to extrapolate the drop in the table to a different flow?
Ok so another development here, just for fun I took a temp reading from the bottom plate of my water jacket. The bottom is hotter then the top.
Here's the back of the boiler just under my lower port.
View attachment 221220
And heres the front of the boiler right next to the fire box.
View attachment 221221
So with that in mind I don't think pulling from the lower ports would be a good idea for the cavitation fix. Lol
I'm thinking the only option is keep pulling from the top and then dropping the pump lower to the floor. What do you guys think?
No, it doesn't work the way you wrote it. Any of the piping above the atmospheric water level in the boiler does not add head to the pump, only friction loss from the lengrh of pipe. The head is negated by itself. The reason is you are lifting (rather, sucking) the water up on the one side and then adding it on the down side. Net change in ststic head is zero, only more fruction loss from extra pipe. That is why the reference is from centerline of the pump to the water level exposed to atmosphere. Only way to circumvent this is raising the water line exposed to atmosphere.I understand the concept in that drawing. Basically you draw up like a siphon then it goes down to the pump and you gain that much more column of water. But how well does it work I wonder? If it works great I'd be willing to try it beings how I'm going to be replumbing the suction anyway. I'd like to hear what others think on that illustration.
No, it doesn't work the way you wrote it. Any of the piping above the atmospheric water level in the boiler does not add head to the pump, only friction loss from the lengrh of pipe. The head is negated by itself. The reason is you are lifting (rather, sucking) the water up on the one side and then adding it on the down side. Net change in ststic head is zero, only more fruction loss from extra pipe. That is why the reference is from centerline of the pump to the water level exposed to atmosphere. Only way to circumvent this is raising the water line exposed to atmosphere.
That makes sense. back to the original plan of just dropping the pump.
Did you happen to come across anyway to tell if the pressure drop through that 90 plate HX would kill me at 10 gpm feeding it?
Your boiler is going to steam, not good!!
If you lower the high limit to 160 and the low limit to 140 being summer operating temps
your going to have many fewer problems.
If you do that you can leave your circulator and its suction on the bottom using a much
larger circulator at a lower pressures and temperature.
When your circulator suction is not flooded you are inviting quick circulator failure.
You need at least one set of isolation valves with gauge ports.
This is to to keep track of outlet pressures P.S.I.G. on your circulator and you need to
have an isolation valve with a port for a vacuum gauge to be sure you are not cavitating
which will destroy the circulator.
You have to remember that if your circulator inlet is that high in the water column it will love to suck in
air bubbles that have not dissolved as air is lazy and will go everywhere.
I use Summer operating temperatures in my coal stoker all winter and they are set
at 140 low 160 high with a fifteen degree differential.
If your flashing to steam at the impeller that always indicates cavitation problems due to
lower inlet pressures(vacuum) you need to move the circulator to the bottom to have
better flooded suction without having it go to steam at the impeller inlet and lower your
operating temperatures.
With storage you already have thermal mass and it takes less energy to heat the
water up to temperature and using summer temperature settings allow the system to
respond faster too as the high limit is lower.
You could use 160 low and 180 as the high limit with no issues.
I use Summer operating temperatures in my coal stoker all winter and they are set
at 140 low 160 high with a fifteen degree differential.
If your flashing to steam at the impeller that always indicates cavitation problems due to
lower inlet pressures(vacuum) you need to move the circulator to the bottom to have
better flooded suction without having it go to steam at the impeller inlet and lower your
operating temperatures.
With storage you already have thermal mass and it takes less energy to heat the
water up to temperature and using summer temperature settings allow the system to
respond faster too as the high limit is lower.
You could use 160 low and 180 as the high limit with no issues.