@warno, to also have four 45 elbows, not two. Don't forget about the two you used to make the turn out of the boiler jacket.
Oh yeah. Changed it here.
@warno, to also have four 45 elbows, not two. Don't forget about the two you used to make the turn out of the boiler jacket.
I have looked through B&G tech manuals for this pump but no NPSH data was available. I would give their tech line a call and ask if they can provide it.@Marshy and here is with length added and pipe size increase. I thought it was posted in this thread but i can't find it, does anyone know the NPSH for the NRF-36 I'm running. I checked the manuals that supplyhouse.com offers but couldn't find it. Unless i over looked it.
View attachment 221044
View attachment 221045
I guess I left my brain at home when I was look at the numbers. I have to agree with you. We are probably using the calculator wrong. I'll play with it or have to break down and do it manually (been a little while, would be good practice).On smaller circulators generally they provide a chart like this. So at 190F you need 2.2 psi on this Grundfos. I've see 4 psi on other brands and models at 190F, depends on the type of pump to some degree.
I'm of the opinion a 4' volume of water above the circ is around 1.7 psi. Hence the cavitation potential in your case.
Here is the explanation for static pressure calculation.
As we all suspect Warno is on that fine edge with his static and cavitation, he has about 1.7 psi, the pump would like 2. Since he cannot change the pressure change the temperature is his only viable variable.
No, very unlikely. If it was then the pump wouldn't actually pump anything it would become air bound. As the fluid enters the eye of the pump the pump is creating a low pressure from the suction of the impeller. That low pressure is localized right in front of the impellar close to the moving vanes. Its just enough for some of the fluid to flash to vapor. It then recombines to liquid when it reaches a higher pressure, usually in the volute of the impeller. The collapse of the vapor bubble gives the noise you hear and can damage the surface of the impeller.If I take a pressure reading on the suction side of the pump it would be vaccuum reading right? Or no?
I have a port on my suction side i can put a gauge on if this information would help us figure this out. And there's another port i can take a reading at the return just before going into the boiler.
View attachment 221052
@Marshy so there is a positive pressure reading at the suction side of the pump. I understand with the pump not running you would see the pressure from the water weight but if the pump is drawing water down the pipe is it still reading positive pressure? Would a pressure reading at the suction side of the pump tell us anything we need to know?
Keep tuned in @maple1 we're going to get this. Lol
So I would like to switch gears. I'm understanding my pump is going to be flirting with caviation basically no matter what I do besides running lower temperatures. I'll go ahead with the lowered pump location like talked about before and I'll plumb in the larger piping for good measure.
But what I just realized, took me 2 years, is my FPHX is killing the heat transfer no matter what I do. It's only a 20 plate that measures 4 1/4" x 12" x 2".
So my question is is it possible to hit a target of mid 180s with a HX that measures 5" x 12"? What plate count would that take? I haven't seen a 5 x 12 option on flatplateselect.com. I'd really like to stick with getting one from eBay and those are the dimensions that are in my price range for a new HX.
36.8 square feet of heat exchange surface is what you need for those conditions. I can't say for certain all brands are manufactured to the same quality or performance.
that should do the trick.