I thought you said it was a single speed. My bad, I'd recommend running it on low and not messing with the plumbing at all. Any reason you would need the higher flow?Watching a fire burn right now.
Reading right on the pipe going into the pump is 199°F. With the pump on speed 2, I get cavitation. With the pump on speed 1, there's nothing.
I'm reading a 25° delta T at my plate HX on the boiler side.
The pump is a bell and gossett NRF-36.
Should I still go through with the replumbing in the boiler shed or just run on speed 1?
Let me see if I understand this. You have a 25F delta from boiler outlet (199F) compared to the cold side outlet of the htx? Or was thst measured at the return pex in the boiler cabinet?
What's the temp drop from boiler outlet to htx inlet (ie loss between boiler to htx)?
What's the temp drop from the cold side of the htx to the return in the boiler cabinet?
Pick your poison I guess, running on low speed or on medium and throttle the discharge slightly if you need a little more flow. Even throttled on medium it's probably more flow than slow speed unthrottled.