master of sparks said:What turns on pump "A"? Does it turn on with the 140f control on the EKO? If so what if the tanks are at 180F and the boiler hits 150F from a cold start?
Also, depending on the flow pattern through that 3 way zone valve it LOOKS like the two pumps will be in series when the ZV flows straight though?
Also what causes flow into the buffer tanks?
master of sparks said:What are the temperature requirements of the heating loops? I'd guess you want 160F or more if the heating emitter are baseboard or fan coils. Maybe 140F for panel rads.
So the upper thermostatic valve would be set to 160, let's say. Really the indirect would be better back at the boiler loop via closely spaced tees for the hottest, quickest supply. If the upper thermostatic is set to 180 so the indirect tank could get plenty of BTUs, then why have a thermostatic there at all if 180 is desired for all the high temperature loads?
I'm still unclear on how or what regulates the flow through the buffer? And does the flow direction change through the buffer when the boiler circ is off to "unload" any heat from the buffer? Or will the buffer always run at the boiler temperature? The pressure drop through the upper 3 way will always be higher then the pressure drop through the buffer. Seems like a balance valve may be needed to assure the 3 way gets enough flow to supply it's loads?
I guess what is needed is some temperature numbers and required gpm through the various circuits to really get clear on flows at various loads on or off.
hr
tuolumne said:Right, if the DHW is calling, pump B is running. However, the other zones are using any hot water, so pump B starts cycling in the red loop endlessly. Oops. If I move the pump to the left of the hot demand zones (actually drawn this way in my 3D layout) the mixing valve won't work right....will it? I almost need a primary seconday loop off the primary loop....too many pumps gobbling up kilowatts. I don't really care about my radiators running short cycles at 180 degree water as much as charging the buffer at the same time when heat is available. With your primary/secondary diagram, I don't see how I can draw off the buffer in reverse for retrieval.
tuolumne said:I am not sure the sidearm will work now that I've laid out the equipment. I need to run my main loop way out of its way to do the sidearm. I have a superstor ultra 80 gallon tank. My plan is to pipe in the boiler loop which is known and get my tanks set to see where things are at. I need some concrete progress to help clear my head!