tuolumne said:
Thanks for getting me past that plumbers' block nofossil. Here is the simplified version, with a mixing valve to send 140 degree water through the primary loop. The varying amounts of return water diverted back to the zones will cause the boiler pump to charge the tanks all of the time. Back to some of the original questions...where do I need check valves, isolation valves, drains etc. Where in this scheme should I put tees for a future fossil fuel backup?
I just thought of a small problem...I would still like the indirect DHW to get supply water as hot as possible. Also, I may be putting a hot water unit heater in the garage at some point, and when I want it on it will be with little notice and also need hot water. Just when I thought I could see bottom the water starts getting murky again.
You've sketched exactly what I was thinking. I'd make a drawing change to make it more intuitively obvious what's going on - I'd put the tanks one above the other, with the cold connection below the bottom tank. The tanks participate in both loops - te left loop with the boiler, and the right loop with the heat loads. If they 're drawn in the middle that way, it makes the two loops more obvious, and it also clarifies the thermal stratification. Ideally, you'll have a sharp thermocline that moves downward through the tanks in sequence as you put in heat, and moves back upwards as you withdraw it. I don't know how much you can avoid mixing, but commercial systems go to great lengths to promote stratification. Pipe fitting selection and location might be all you can do.
Now that you've made the drawing change, move the expansion tank out of the way and stick a fossil fuel boiler in there with its own circ drawing from the cold return, so that it's in parallel with the tanks and the EKO.
Both boiler circs need check valves. I'm hoping that the secondary circ won't suck water through the boiler(s). Probably the best approach is to plumb it so that it has an independent connection to the top storage tank.
I like an isolation valve on each side of each boiler. Make sure you have a relief valve inside the isolation valve. Boilers have their own drain valves, You probably want isolation and drain valves on the tanks too.
Perhaps you could move the DHW loop so that it straddles the mixing valve. I'd also consider if possible setting up a sidearm HX for the DHW, probably in the hot supply line just to the left of the top storage tank. That way, any time that either boiler is running, your DHW tank is getting superheated (you DO have a tempering valve, right?). The DHW circ will only run when the DHW tank drops below its setpoint. My DHW hasn't called for heat since October.
If you're heating a remote load such as the garage hot water, use 1/2" pex. For intermittent loads, the loss from the slug of cold water that you have to push through can be a big deal.