spudman99
Feeling the Heat
I can address this problem with some certainty. My princess insert on a 30' exterior masonry chimney and is insulated.
I have a magnehelic installed to monitor draft. When cold my draft reads 0.02wc ("water column in inches"). On a cold day with fire on hot my meter pegs at more than 0.25wc, which is 3x or more above BK specs. My stove is still controllable at that high draft, turning down the thermostat to low will almost immediately extinguish the flames.
I can control the heat output throughout the full range of the thermostat. When I put it at medium I can get the combustor gauge to the middle and stay there, fan on medium also. I can also peg the gauge on high with the fan on high if I so desire.
During a normal burn of lets say 75% closed on the tstat, temps outside in the 20's, full load and active cat, my draft runs in the 0.15-0.18 range continuously.
So the answer is from a real field installation of a nearly identical stove with similar operating infrastructure is that the unit is controllable. There is something wrong with the thermostat, perhaps something holding it up so it doesn't close completely? I think I remember a thread last year where there was a screw that interfered in the thermostat closing fully (mellow?) which after correction eliminated the problem. Could that be an issue here?
I have a magnehelic installed to monitor draft. When cold my draft reads 0.02wc ("water column in inches"). On a cold day with fire on hot my meter pegs at more than 0.25wc, which is 3x or more above BK specs. My stove is still controllable at that high draft, turning down the thermostat to low will almost immediately extinguish the flames.
I can control the heat output throughout the full range of the thermostat. When I put it at medium I can get the combustor gauge to the middle and stay there, fan on medium also. I can also peg the gauge on high with the fan on high if I so desire.
During a normal burn of lets say 75% closed on the tstat, temps outside in the 20's, full load and active cat, my draft runs in the 0.15-0.18 range continuously.
So the answer is from a real field installation of a nearly identical stove with similar operating infrastructure is that the unit is controllable. There is something wrong with the thermostat, perhaps something holding it up so it doesn't close completely? I think I remember a thread last year where there was a screw that interfered in the thermostat closing fully (mellow?) which after correction eliminated the problem. Could that be an issue here?