Are we sure we didn't move any wires from their original position? RIB relay gets wired in parallel with the actuator.
You are correct. I pulled the thermostat wires. I am on my way downstairs to correct it. I'll let you know.
Bob
Are we sure we didn't move any wires from their original position? RIB relay gets wired in parallel with the actuator.
The RIB will stay constantly lit when powered correctly. What I'm trying to do is get the RIB to close T-T on the Aquasmart when the 3 way valve is set for flow to the Buderus. We can do it a few different ways. We need to know what terminals have power on the 3 way valve and when (what position). The RIB has normally open and normally closed contacts allowing us to do it a number of different ways.
We'll get this sorted out Bob, I'll digest your last post and we'll come up with a plan.
Pt. Jeff isn't far, less than ten miles, I'm in Ridge.
Enjoy your Christmas as well.
Ron
Ron,I think I have Office on one of my pc's, I'll sure try.
Scratch that. It wouldn't let me drop the file in the message. Can you send me an email address?Ron,
I sent the info in a message.
Bob
What was the fix?it appears we've found a fix that Mr. McKraut can live with