Can probably get this wired in to solve your issue.
http://ribrelays.com/Products/Pilot-Relays/RIBU1C.html
http://ribrelays.com/Products/Pilot-Relays/RIBU1C.html
Can probably get this wired in to solve your issue.
http://ribrelays.com/Products/Pilot-Relays/RIBU1C.html
like to see the manual of the 3 way valve.
I attached the actuator product information.
Attached Files:
How about the model number of the zone valve and a real world photo of the valve itself. This is a wiring issue probably solved in about 10 minutes. The manual shows SPDT and SPST type valves, all of which have 6 terminals on the valve.
I attached the info for both the actuator and the 3 way valve. If you need a picture of the valve in the system itself, I can get one for you in a few hours. I just finished scrubbing the basement floor and it will be dry in about an hour. Just came up to get something to drink and saw the post.
Thank you,
Bob
Guinness? I'm a Smithwicks fan myself.
Was there some reason you thought the diagram above would not do the trick?[Wiring diagram upsthread]
Was there some reason you thought the diagram above would not do the trick?
I see what you're saying. I was seeing an end switch where there isn't one. Does there need to be a DPDT (DPST) activated by the Tekmar stage-two contacts, on pole to activate the valve actuator and another to close T-T to the aquastat?Shouldn't his three way valve have white, orange and grey wires for an end switch. I haven't seen them in any part of the thread yet. Maybe I'm missing something? If the valve is missing the end switch you can make one with a RIB relay, I do it all the time. I just can't see buying an unnecessary relay, if the end switch is there. The Tekmar and Aquasmart should be isolated in my opinion as they each have their own 24 v transformer.
I see what you're saying. I was seeing an end switch where there isn't one. Does there need to be a DPDT (DPST) activated by the Tekmar stage-two contacts, on pole to activate the valve actuator and another to close T-T to the aquastat?
How many wires or terminals do we have on this three way valve, and what might they be labeled or colored? I believe that the three way valve is "not talking" to the Aquasmart. We need to open a line of communication, in the mean time I'm going to have a Smithwick's.
The Series 20, 40, and 80 all have blue, brown, and black wires. Series 20 uses SPDT control, series 40 and 80 use SPST control. I don't think we can tell what type of actuator it is just by the color of the wires. Or did I miss upthread where the type of actuator was identified?The 3 wires are blue, brown and black.
So the 401 accumulates error on the supply header sensor and activates stage two high fire, but there's still a call for heat to the wood boiler on stage one, is that right? But on high fire the three way valve shuts off flow from the wood boiler so it shuts down on high limit.The three way valve seems to be without an end switch. A RIB relay will emulate an end switch. With the powered side of the RIB wired to stage two on the Tekmar and the other side wired to T-T on the Aquasmart. Problem solved $10.
So the 401 accumulates error on the supply header sensor and activates stage two high fire, but there's still a call for heat to the wood boiler on stage one, is that right? But on high fire the three way valve shuts off flow from the wood boiler so it shuts down on high limit.
Meanwhile the oil boiler comes up to temperature from a cold start, brings the supply header back up to setpoint, and then the 401 goes back to low fire. If wood boiler can respond quickly enough to satisfy demand going forward we're good, else cycle repeats?
Seems like the wood boiler could spend a lot of time ready and willing to supply heat, but the 401 will keep it valved off when it's most needed.
I'm using that 3-way zone valve and actuator with a tekmar thermostat. They go through a taco zone valve controller. Taco had a bigger PDF that showed how to wire up all their pump and zone valve controllers. That is what I used to find out how to wire mine. I'm sure it was from the main taco website.
I had (on page 60) Honeywell VC 40 & 80 (spdt) hydronic zone valve with taco zone valve control. I only copied that page.
I could go look at the color of my wires later if It will help.
The Series 20, 40, and 80 all have blue, brown, and black wires. Series 20 uses SPDT control, series 40 and 80 use SPST control. I don't think we can tell what type of actuator it is just by the color of the wires. Or did I miss upthread where the type of actuator was identified?