How much pipe (and what kind/size) do you have between you boiler and storage? You should be getting significantly less idling now as opposed to the balancing valve fully open. I suspect if you have a fair amount of head loss in you piping to storage then you will have to close down the bypass even more. Just be careful you don't close it down too far or you will end up with the situation I described previously.
If you close the balancing valve all the way, the termovar will shut down the feed from storage in an attempt to regulate the boiler inlet temperature. In this condition you will not have much flow out of the boiler and should have a lot of idling.
The mixing will never completely stop due to the design of the termovar. It never closes off the bypass port, even with temperatures over 160 coming from storage.
The reason behind the balancing valve is to provide additional resistance to the branch of the loop. From the perspective of your boiler, the bypass and storage look like 2 loops in parallel. The loop with the least resistance will get the most flow. If you have a long loop or something creating a lot of pressure drop in your storage loop, the majority of the flow will head for the bypass until it is closed a fair amount.
I get idling with my tarm 40 when the bottom of storage is at 150 - 160 depending on how much heat the burn is producing. It does not idle for long at this point. I suspect it would not idle at all if the bypass was completely closed - I have always wanted to try using a zone valve with a cheap temperature controller to close off the bypass loop under these conditions.
Your system is idling because you cannot get the BTUs out of the boiler fast enough at these return temperatures. I suspect this is a combination of how much is going though the bypass loop and the characteristics of the pump performance and the storage loop.
BTW, I checked my termovar and it is also stamped 72 C. I believe this is the temperature where the storage port is fully open, but I may be wrong.
If you close the balancing valve all the way, the termovar will shut down the feed from storage in an attempt to regulate the boiler inlet temperature. In this condition you will not have much flow out of the boiler and should have a lot of idling.
The mixing will never completely stop due to the design of the termovar. It never closes off the bypass port, even with temperatures over 160 coming from storage.
The reason behind the balancing valve is to provide additional resistance to the branch of the loop. From the perspective of your boiler, the bypass and storage look like 2 loops in parallel. The loop with the least resistance will get the most flow. If you have a long loop or something creating a lot of pressure drop in your storage loop, the majority of the flow will head for the bypass until it is closed a fair amount.
I get idling with my tarm 40 when the bottom of storage is at 150 - 160 depending on how much heat the burn is producing. It does not idle for long at this point. I suspect it would not idle at all if the bypass was completely closed - I have always wanted to try using a zone valve with a cheap temperature controller to close off the bypass loop under these conditions.
Your system is idling because you cannot get the BTUs out of the boiler fast enough at these return temperatures. I suspect this is a combination of how much is going though the bypass loop and the characteristics of the pump performance and the storage loop.
BTW, I checked my termovar and it is also stamped 72 C. I believe this is the temperature where the storage port is fully open, but I may be wrong.