Yes I do have that T-stat wired up.
It came with it..
I also have tried a Honeywell Programmable (not wire-less)
Thank you for confirming the wiring!
I felt I had that right.
I've read some programmable's need 24v line voltage to run..
Anyone know what the line voltage is?
I'm going to put my DMM on it and check myself today.
I also have an older one upstairs that is only used as a thermometer...
May switch that one and try. (but I need clean start ups)
Whatever your stove is it is likely a millivolt system. The stove is looking for a switch, your stat provides that switch, you need a stat with a swing to it so it isn't short cycling the stoves ignition systems or the stat needs a cycle length enforcement system to reduce the number of cycles the stove is put through. . The voltage across the stat terminals at the stove end can be under a volt. You will be hard pressed to operate any stat that actually requires power from the stove.