ambene said:
SmokeyTheBear said:
ambene said:
SmokeyTheBear said:
ambene,
If you have some electrical tape around we can further verify that is the problem.
That 160 degree snap disc that is showing up as always closed can be removed from the circuit by placing electrical tape on the lead you removed to do the continuity test and the stove manually fired at a low heat level setting, allowing the stove to come to temperature the blowers and auger should operate and then turning the stove off.
It should proceed to normal shut down.
Did you also do the test with the 140 degree snap disc?
I did not do the test with the 140 but I will now. A question, if I remove the 160 disc completely from a cold stove, shouldn't the stove shut off?
I don't know what the logic being used by the controller is.
The controller has to see things the way it expects them to be and also in the order they open and close.
Most stoves use only one switch to indicate fire in the device, this is why I asked about the 140 degree switch in particular as that is normally the one that indicates a fire in the stove.
At the moment I'm only interested in switch states.
I have my switches mixed up, I was looking at pictures instead of the blow up diagram. When applying the multimeter leads to the 160 switch (mounted against the firebox) the multimeter never moves from 1 no matter where I place the leads. I removed one purple wire to test it and then the other, neither moved from 1. When applying the multimeter leads to the 140 switch, (mounted against the combustion blower assembly) this is the switch that reads all over the map and then returns to zero.
The one on the combustion blower is the one that is causing you the trouble, it should close only after the temperature reaches 140 degrees and it is likely supposed to open at 120 degrees.
I'd order a new 140 degree switch and if you can get a ceramic one. They generally last longer.
The 160 degree switch appears to be the one that causes the convection blower to go to high speed if needed.
I don't like telling folks to remove wires while a stove is running it is just too dangerous. But if the fan runs the moment you plug the stove back in, then you can insulate one of those leads on the 140 degree switch when the stove is unplugged and cold and then plug the stove back in. That should stop the fans.
I have a healthy respect for electrical devices and observe some rules that seem funny to others.
Been bit by devices that have been powered off and unplugged before.