oldspark said:
davmor said:
oldspark said:
davmor said:
You cannot have your subpanel ground and neutral bonded. It appears that is what you have done. Not sure on your questions. Maybe a picture of your main panel may help. If you are not sure of your work you may be farther ahead to have someone look at it.
I hope not as it has been beat to death in this thread, I can not tell for sure from the picture.
If you click on the picture it enlarges it. It looks like the the neutral and the ground are on the same bus bar.
Right you are, don2222 did you catch that, that is a no no and mentioned in the thread many times. The one link I posted had every thing covered for a sub panel. Good eye davmor!
Hello oldspark
Yes, but was not clear about why. So these two links explain it! Thanks for pointing me in the right direction!
There is an optional ground buss for this panel and it did not explain anywhere what this option was for!
I now understand the extra buss is for equipment ground that this panel feeds that should be connected to a ground rod outside the shed
What I need that can be purchased at ACE hardware is:
(broken link removed)
Then a ground wire must be attached to this ground buss outside the shed!!
from
http://masterslic.tripod.com/FAQ-2/18.html
Why isolate the neutral in a sub panel?...
The neutral is only bonded to ground at your service panel. At all other points throughout your house, there is no connection between the bare (or green) grounding conductor and the white neutral conductor. Under normal conditions, the grounding conductor carries no current. No current means there is no voltage drop along it, therefore anything "grounded" to this conductor is at the same potential (voltage) as ground. If you bond the neutral and ground at the sub panel, then stray currents from the neutral return could go thru the equipment ground on the electrical devices fed from this sub panel. If you isolate the neutral and ground at the sub panel, than any currents would go back to the main panel, and go to the service ground. The main panel is where the neutral and equipment ground should be bonded.
If you install a sub panel outside the building from the main panel, than you will need to drive a ground rod at this panel. A single branch circuit run to another building is not considered a sub panel.
also from here
http://ths.gardenweb.com/faq/lists/wiring/2005015726007600.html
Grounding and bonding of the sub-panel
At the sub-panel there must be no connection between the neutral bus bar and the equipment ground bus bar or the neutral bus bar and the sheet metal of the breaker box. You may need to purchase an additional bus bar for the equipment ground since many panels, especially those that come with a main breaker, do not come equipped with one. If the panel comes with a bonding screw or bonding strap, do not install it to the neutral. Depending on the brand of panel, you may need it to connect the ground bus to the sheet metal enclosure.
At the remote building, you will need to drive two eight-foot ground rods located a minimum of six feet from each other and connect them to the equipment ground bus using #6 copper wire. The easiest way is to make one continuous run without cutting the wire. The rods must be driven in flush or below grade. The ground rod clamps must be listed for direct burial. It will say so on the clamp or look for the letters "DB". If you have any metal piping (except gas lines) in the remote building, you must bond it to the equipment ground bar, use #6 wire. If the connection is to a metal water line, the connection should be within the first 5 feet of where the water line enters the building. All connections must remain accessible, so if the connection will end up inside a wall, you must provide an access plate.
I realize that some of the things I've included exceed the code minimum, but this is an attempt to make a "one size fits all" response without getting into a really long discussion.
For a sub-panel in the same dwelling there is no need for additional ground rods or connections to metal piping. Also, no need for a main breaker in the sub-panel, regardless of the number of circuits. Unless you are running metal conduit, you will need to run a 4 wire feeder.
------------------------------------------------------------------------
Ace Hardware Equipment Ground Buss for Sub Panel in shed!
"SQUARE D" GROUND BAR KIT
For attaching ground wire in load centers and safety switches
Required when load center is not at point of service entrance
Has 12 lugs in grounding bar
For wire diameters between 4-#2/0 AWG maximum
UL listed
Clampack
Fits Ace No.s 32537, 32538, 34034, 34035