Sorry for the rant. To see the actual numbers and images of the air moving it just shows dollar signs heading out into the atmosphere.
Dude, rant away. In fact, I'll see your rant and add another.
This is the first house we've owned in which combustion appliances are housed within the conditioned living space. The gas furnace and the gas water heater are both in the laundry room, side by side. They vent into a shared chimney.
During the home inspection, my father-in-law, an engineer, and the home inspector stared at the water heater vent for a good long time. It has a horizontal traverse to the place in which it exits the wall to vent into the chimney. It does have a vertical rise along the the length of this traverse, but it also has a bend in the pipe to accommodate the horizontal movement, and the bend is relatively close to the hood over the actual water heater. Yadda yadda.
They did some calculations and decided that the vertical rise vs. the horizontal traverse met code, but there was talk of drafting and back drafting. The two guys decided that the homeowner had left the window in the laundry room opened so that the water heater would draft efficiently. They recommended leaving that window cracked all the time, so that the water heater would draft, efficiently. I noted that the laundry room bone was connected to the rest of the house bone and that the entire skeleton would freeze, or get very hot and humid depending on the season, and that the entire skeleton would likely object to the impact of a continuously opened window on the utility bills.
They then recommended that we keep the window in the laundry room opened all the time and the door to the laundry room closed all the time.
*Insert Lay Person Secret Eye Roll at Engineering-Types HERE.*
I looked around at the situation, at the room, at the house, at the water heater, at the vent pipes, and I seriously doubted that the home owner left the window in the laundry room opened so that the water heater would draft efficiently. I decided that the homeowner had left the window open in the laundry room because she had a cat and the cat's litter box was in that room. She left the window opened just in case Kitty dropped the Poo Bomb after she left the house.
So when we moved into the house, I parked a CO alarm in the outlet right next to, as in almost touching, the water heater and went on about my life. The idea that the water heater's vent may not be drafting as efficiently as it should never completely left my mind, but we kept the dual powered (a/c and battery back up) CO monitor right there, and we changed the batteries twice a year, faithfully, and life went on.
The CO monitor never uttered a peep.
Of course, the house was so, ahem, "breezy" that we were self-ventilating.
Now that we are seriously, seriously sealing up this house, the idea of the water heater vent loomed larger in my mind. First of all, we calculated the age of the two CO detectors that we have here- one in the laundry room with the furnace and the water heater, one in the stove room. Both were over 5 years old, so we replaced them.
Then we revisited that water heater vent. I did a "stress test" with exhaust fans running, the dryer running, the furnace running, and the water heater fired up, and it appeared to back draft- it fogged a mirror that I set next to the hood.
I called our HVAC company immediately. They also deal with gas water heaters and they came right out.
Turns out that I didn't let the water heater run long enough before I popped the mirror up next to the hood. Once the vent pipe heated up, the water heater drafted just fine- so well, in fact, that the HVAC company's much more sensitive CO monitors (they tested with two different types) picked up zero to negligible parts per million CO at the vent hood. We did the mirror test again, and with the water heater (and everything else, exhaust fans, furnace, dryer) running full tilt, and the mirror did not fog.
Here's what we didn't see coming:
The *other* end of the water heater's vent pipe had become, at some point in the past, unsealed from the wall.
The terminus of the vent is tucked up in a corner on the other side of the air handler, which is on top of the furnace. To say that I don't routinely pay a lot of attention to that remote corner of the house is an understatement. I don't do a lot of deep cleaning behind the furnace. I vacuum all around it, I mop the floors, etc.- there's no debris built up back there- but I don't routinely "dust the furnace" or the vent pipes where they duck behind the air handler.
Our HVAC tech was inspecting the vent pipes and all of the sudden he said, "WHOA! LOOK AT THOSE COBWEBS!"
I'm a little particular about my house keeping, dark undersides of the furnace and air handlers not necessarily included in that compulsion, so I took exception. "WHAT COBWEBS? YOU FOUND COBWEBS? STOP STARING AT MY COBWEBS! IT'S NOT POLITE!"
HVAC Tech said, "No, not worried about the cobwebs- look at the air movement! Your gas water heater vent has come unsealed at that end!"
So while I'm all worried about the hood end, the other end has pulled itself out of and away from the wall- enough that the combustion gases rising up the vent were causing those rogue cobwebs to flap in the breeze.
The HVAC Tech had used all the sealant in his truck but he post haste went to the plumbing supply store, bought more sealant, came right back to the house and sealed that vent.
I have no idea how much CO was spilling from that end of the vent but it couldn't have been too bad- the CO alarm never went off, and never registered any number other than zero at any time that I looked at it.
I do wonder how much of our heated and cooled conditioned air went up our chimney through the rather large gap left by the duct coming unsealed from that opening in the wall. Even though that hole is tucked back behind the air handler there is some room for air flow back there- and it is located, unobstructed, in the conditioned envelope of the house. It would be the equivalent of having a pretty big hole in your exterior wall- or, as my father-in-law and the home inspector said, "Leaving a window opened."
While I feel a little foolish for calling our HVAC guy, God love him, to our house to measure zero to negligible CO levels, that was a good catch, and we will probably make the cost for that service call up in short order by not sending heat up the chimney through a hole in the wall.