Referencing the diagram, please note what needs to be done.
Almost there. Since you are choosing to keep the LP boiler hot (which is a valid choice), the supply line from the coal boiler should be connected to the supply side of the LP boiler, and likewise the returns should be connected together. But the supply side connection would need to be somewhere on the inlet side of the the LP boiler pump, P2.How about this? I don't know if I need both check valves though.
The aquastat relay would be wired to the coal boiler T-T terminals in addition to all the system call-for-heat contacts, all 'wired-OR' together.Then if you wanted to eliminate the chance of that stuff circulating cold water from the coal unit if it ran out of coal or something like that, you could also use one of your 4006 stats (whichever one makes on rise) sensing at your coal boiler, that would interrupt the electricity between the Johnson & P1 if the coal boiler went cold.
OK, new diagrams, original setup shows some return lines from the rooms - they are of course shortened down. I also have two proposed changes. What I believe are a series setup, and parallel. It seems that the installer set it up as a parallel system - almost, although I believe that wasn't what he told me he was going to do...
This is the setup as it is NOW.
View attachment 142325
This I believe changes it to run in SERIES.
View attachment 142326
This should be the setup in PARALLEL.
View attachment 142327
OK, could someone tell me what I would be missing to install where in the series and parallel examples above? The original installer is supposed to come over tomorrow at noon to fix this debacle.
First, thank you!Does the coal fired boiler provide the DHW with a tankless coil somehow?
Not sure why series piping is required if DHW is not provided by a "hot" boiler?
Super simple ways to parallel boilers without pumping and flow conflicts.
Here are some piping examples. The tank or separator, in the drawings may not be needed or wanted, just install the ZVs there, like the hand drawn example.
I would protect the coal boiler with a mix valve.
A link to a journal that may help the installer with the concepts.
http://www.caleffi.com/sites/default/files/coll_attach_file/idronics_10.pdf
Ignore all this if for some reasons the boilers MUST be series piped.
Thank you!Using the third drawing, just move the LP boiler pump up above the tee that feeds over to the return side of the coal boiler and your're good to go.
=======I was laying in bed this morning figuring this all out, then I come on here & see you guys are ahead of me.
I have a question though to add to the dialogue - what exactly do you have for circ pumps now at each location?
I am guessing the propane circ is a constant speed pump that is flowing too much flow for when just one or two zones are open. You would see much better zone (and maybe also system) performance if that pump (P2) was a Grundfoss Alpha or the such - and I would hazard a guess that your water hammer issue would disappear. You could possibly reduce control issues using an Alpha there also - just plug it into power, it will sense zones opening & closing on its own and maintain proper flow, once you get the baseline flow (delta P) tuned in.
Referring to ewdudley's help above, you could use a Johnson A419 controller to control the call for P1 to start & stop, and surface mount the sensor for it on the LP return pipe, as far in towards the boiler as you could get it. Or onto the surface of the water jacket itself, at the return tapping - depending on access to the jacket. Then if you wanted to eliminate the chance of that stuff circulating cold water from the coal unit if it ran out of coal or something like that, you could also use one of your 4006 stats (whichever one makes on rise) sensing at your coal boiler, that would interrupt the electricity between the Johnson & P1 if the coal boiler went cold.
Also don't know exactly what kind of setup that is for DHW off the coal unit? And it still looks like your expansion is on the wrong side of the circs - that said without knowing distances between everything though. How far apart are the boilers? Thinking you likely would only need one expansion tank setup for the system.
OK, new diagrams, original setup shows some return lines from the rooms - they are of course shortened down. I also have two proposed changes. What I believe are a series setup, and parallel. It seems that the installer set it up as a parallel system - almost, although I believe that wasn't what he told me he was going to do...
This is the setup as it is NOW.
View attachment 142325
This I believe changes it to run in SERIES.
View attachment 142326
This should be the setup in PARALLEL.
View attachment 142327
OK, could someone tell me what I would be missing to install where in the series and parallel examples above? The original installer is supposed to come over tomorrow at noon to fix this debacle.
The transformer is on the lp side, so the zone valves are powered by that, and t-stats. No, I believe the arrows are correct, since I open the zv manually then it gets hot immediately above it.The zone valves shouldn't be powered by a boiler - they should be powered by the thermostats.
Edit: aren't those red arrows in your zone flows pointing in the wrong direction? And if you just discovered that pump was pumping the other way, does that mean the valves are installed backwards? Would still like to know what you have for a circ there.
That would take care of the DHW reserve problem nicely, which removes the main advantage of going with the figure-eight.On the DHW thing - I assume that setup is a tankless coil in the coal boiler, in series with an electric hot water heater? Don't think that has been clarified for sure. If so, I think there are a couple of ways to improve that situation. First, don't mix down between the coil & electric heater as shown. Rather, put a mixer on the DHW-out of the electric water heater, between it and the taps. If that was still not satisfactory, you would for certain have all the hot water you would need if you added a small recirc pump (I have a B&G Ecorcirc E^3) that would circulate the water between coil & heater when there was no hot water being used. I control mine with a Johnson A419 in a FPHX setup. Also don't know how big the electric heater is either - but the bigger the better for that, if a lot of hot water is being used.
@layoric: How about a close up well lit picture of the LP boiler pump so we can see for ourselves what direction it is pumping.No, I believe the arrows are correct, since I open the zv manually then it gets hot immediately above it.
How can that be, if the pump is pumping down?
Ahh, but the coal boiler pump P1 is pumping up in the as-currently-plumbed diagram!No, I believe the arrows are correct, since I open the zv manually then it gets hot immediately above it.
How can that be, if the pump is pumping down?
What I meant was the zone valves transformer is powered on the circuit on the boiler.The transformer is on the lp side, so the zone valves are powered by that, and t-stats.
OK, I guess maybe I could clarify a little. They may be powered by a transformer on the LP side, but they are activated and controlled by the stats. The stats activate a ZV on call for heat, the ZV opening then starts the circ pumping usually by an enclosed end switch in the ZV. The tranformer power supply is a constant and doesn't really matter where it comes from - it gets switched by the stats. So really neither boiler controls the zone valves.
I think.