Not liking what I'm seeing for flow requirements on the HX. I need to know what water temp you have available in the boiler and what water temp you need to heat your house in order to get a good handle on what flow we have to get through the HX. Right now, using the 50 plate you have, 180 in and 170 out (boiler side) and 155 in/170out on the house side the flat plate software is calling for 14gpm on the boiler side. Does the house heat OK with say 150-160* water temp?
Factoring in all the parameters you listed, I'm seeing the following with a 15-58 Grundfos. 6.9GPM, 13.1 ft of head and a 5.5PSI differential. Throwing a big dog 26-99 or 0011 on it only gets us another 1-1.5gpm and blows the head into the stratosphere. No high head circ is going to live very long on an open system while pushing heads in the 20'+ range.
Here's the bottom line. When I plug the 6.94 GPM into the HX software it shows that we can only transfer about 34,000 btu's given the water temps I listed above. I don't think that's going to cut it for you.
I guess I'd like to say to all who read this that the issues we are running into here are not uncommon at all. Many "pro's" who have been doing this stuff for ages fail to comprehend that all the components have to work as a system rather than just a collection of parts. Typically, the guy selling OWB's just doesn't understand it because he's a salesman not a system design/install person. It ain't rocket science but you have to obey the rules.
Factoring in all the parameters you listed, I'm seeing the following with a 15-58 Grundfos. 6.9GPM, 13.1 ft of head and a 5.5PSI differential. Throwing a big dog 26-99 or 0011 on it only gets us another 1-1.5gpm and blows the head into the stratosphere. No high head circ is going to live very long on an open system while pushing heads in the 20'+ range.
Here's the bottom line. When I plug the 6.94 GPM into the HX software it shows that we can only transfer about 34,000 btu's given the water temps I listed above. I don't think that's going to cut it for you.
I guess I'd like to say to all who read this that the issues we are running into here are not uncommon at all. Many "pro's" who have been doing this stuff for ages fail to comprehend that all the components have to work as a system rather than just a collection of parts. Typically, the guy selling OWB's just doesn't understand it because he's a salesman not a system design/install person. It ain't rocket science but you have to obey the rules.