Noggah said:The circulator is a Grundos three speed. On hi I think it's pushing 11 gallons a minute. I thought about trying a larger one, but have not yet. When I say the boiler is working hard, it runs for long periords. It does catch up, but mainly when the garage is not calling. The retailer thinks I need to remove the heat exchanger, pipe the boiler directly into the loop and run everything at atmospheric. The boiler does have 310 gallons of storeage, so this makes scense. The plumber says that this will void the warranty on my new, New York Thermals propane boiler.
I would heartily agree with your plumber. Leave the HX in place.
Your problem is that the slab is capable of dragging more heat out of the system than the CB is able to replace on a relatively sudden basis. I watched a 3500 sq ft slab drain the heat from a CB7260 so fast that the fire was just nicely ramping up before the boiler protection valve (Termovar) kicked in and started bypassing the slab. I believe that unit is rated at over twice the capacity of yours IIRC and it was over an hour before the water temp in the CB started to stabilize.