I keep thinking I could get more from my system ? My current setup is a Tarm solo 60 and a hybrid storage system of 370 gal. pressurized storage and 1200 gal. unpressurized storage. How it is set up system charges and return temp control by a termovar and a B & G NRF 36 pump = ( grundfos 26-99 ) .
My return comes both from my storage and from my 5 zones to a Tee shortly before the termovar and since I use radiant in floor in 1 zone my return temps before the termovar can be anywhere from 100 to 160 + degrees .
I am trying to keep the solo 60 in the burn more rather than idling but with the big swings in return temp the only way I can do that is by camping out with my balancing valve trying to hold my return temps . The termovar seems to be rather loose in its ability to contol return temps .
I have been told that a loading unit wont help me out because I need a bigger pump then they have because of me charging my unpressurized storage with 3 - 180ft 3/4 copper coils and I need to have at least a 20 gpm pump to handle the solo 60's output .
Just wondering if there are any guys out there that have had better luck with a Danfoss VTC valve or have I been told wrong about loading units not being able to handle 200,000 BTU output with the coils in my storage ?
I typically can use supply temps from storage all the way down to about 135 so my storage be all the way down to about 120 on the bottom of my tank before I recharge . I can have zone returns anywhere from 100 to 160 if they call for heat ,priority goes to zone by weighted gate valves but I still get some flow from storage return when I am burning .
My feeling is that my termovar is just a restrictive T in my pipe.
Your thoughts Guys ?
My return comes both from my storage and from my 5 zones to a Tee shortly before the termovar and since I use radiant in floor in 1 zone my return temps before the termovar can be anywhere from 100 to 160 + degrees .
I am trying to keep the solo 60 in the burn more rather than idling but with the big swings in return temp the only way I can do that is by camping out with my balancing valve trying to hold my return temps . The termovar seems to be rather loose in its ability to contol return temps .
I have been told that a loading unit wont help me out because I need a bigger pump then they have because of me charging my unpressurized storage with 3 - 180ft 3/4 copper coils and I need to have at least a 20 gpm pump to handle the solo 60's output .
Just wondering if there are any guys out there that have had better luck with a Danfoss VTC valve or have I been told wrong about loading units not being able to handle 200,000 BTU output with the coils in my storage ?
I typically can use supply temps from storage all the way down to about 135 so my storage be all the way down to about 120 on the bottom of my tank before I recharge . I can have zone returns anywhere from 100 to 160 if they call for heat ,priority goes to zone by weighted gate valves but I still get some flow from storage return when I am burning .
My feeling is that my termovar is just a restrictive T in my pipe.
Your thoughts Guys ?