I will try to locate a mechanical engineer to discuss thermosyphoning in this context in more detail. I'd like to clarify that the Garn Barn (GB) slab is only 3' above house 1 and house 2 grades, not 30'. I was hoping 30' was a typo in your analysis, but please forgive me if that wasn't clear. I've attached a diagram attempting to illustrate this further. I tried to draw to scale as much as possible. I can draw the houses larger if my writing is too small to be clear. Also, the highest point in the system for house 1 is 5' above the floor of the attic that is above the 2nd floor (23' above the level of the Garn Barn slab) where the 4 and 5 ton LP furnace supply plenums (17x20 and 20x20 WTAHX) are 5' above that floor.
Don't get me wrong, I'd absolutely LOVE to run the hot water from GB to house 1, and back past the GB all the way to house 2 prior to returning to the GB because house 2 only needs ~110F for radiant floor heating. This is how I originally though the system could be designed. I guess the downside to putting both homes in series, aside from the head loss issue, is that if one house is down, both houses likely would be down. Please correct me if I'm wrong, but I would think the most likely reason for the system to go down, assuming a leak-proof, pressure-checked, installation, would be a bad pump. That solution could be as simple as keeping 2 of each circulator/zone valve, one for backup if the corresponding operating unit fails.
Like maple1, I just can't see how to overcome this kind of head loss using small circulators and 1-1/4" or 1-1/2" logstor, much less 3/4" logstor. That's why I thought I'd need to break the install up into house 1 this year and house 2 next year. I guess I could possibly use larger circulators, but I was trying to use small ones if possible because I'm interested in minimizing power consumption in the event that I run the whole thing one day on solar.
As I understand, a reasonable estimate of head loss is:
Head loss = length of the longest loop * 1.5 (to account for resistance of fittings, HX's, bends in the pex, etc.) * 0.04 (all water with no glycol)
Head loss for house 1
560' * 1.5 * 0.04 = 34 feet of head (barn to highest and furthest points in house 1, and back to barn),
where 560' = [230' (GB to house 1) + 50' (distance from buried dualpex up into the attic and all the way over to the 17x20 and 20x20 WTAHX)]*2
Head loss for house 2
900' * 1.5 * 0.04 = 54 feet of head (GB to radiant supply manifolds, through any 300' loop, back to return manifold, and back to GB)
That is a rather large head loss for either circuit alone, much less combined:
34 + 54 = 88 feet of head
BTW, these head loss numbers seem to correlate with the Garn Design Manual. Referring to pages 13 and 14, a system designed with 20F dT's could flow hot water through 0.678" ID barrier pex (i.e. logstor 3/4") at 3GPM and 4.5GPM and deliver 30MBH (4 feet of head per 100') and 45MBH (6 feet of head per 100'), respectively.
At the 3GPM flow rate, a perfectly straight 560' pex pipe would see:
560' * (4FOH / 100') = 22.4 FOH
Similarly:
560' * (6FOH / 100') = 33.6 FOH
900' * (4FOH / 100') = 36 FOH
900' * (6FOH / 100') = 54 FOH
Add 50% of these values to themselves (the 1.5 figure in the calculations above) and you're in the same ballpark
As a side note, another reason I like your system description is that I don't plan to run glycol and the bypass allows for continual flow which would minimize any risk of lines freezing as long as there is no power outage. My planned LP backup generator for house 1 could provide that assurance because I'm running a 200 amp service from house 1 to the GB. The electrician can put all Garn and house 1 circulators, zone valves, etc. on that generator. House 2 already has a gasoline backup generator to do the same there.
Can you please provide some diagrams illustrating how a 3/4" system could be configured to do this?
I will try to locate a mechanical engineer to discuss thermosyphoning in this context in more detail. I'd like to clarify that the Garn Barn (GB) slab is only 3' above house 1 and house 2 grades, not 30'. I was hoping 30' was a typo in your analysis, but please forgive me if that wasn't clear. I've attached a diagram attempting to illustrate this further. I tried to draw to scale as much as possible. I can draw the houses larger if my writing is too small to be clear. Also, the highest point in the system for house 1 is 5' above the floor of the attic that is above the 2nd floor (23' above the level of the Garn Barn slab) where the 4 and 5 ton LP furnace supply plenums (17x20 and 20x20 WTAHX) are 5' above that floor.
Don't get me wrong, I'd absolutely LOVE to run the hot water from GB to house 1, and back past the GB all the way to house 2 prior to returning to the GB because house 2 only needs ~110F for radiant floor heating. This is how I originally though the system could be designed. I guess the downside to putting both homes in series, aside from the head loss issue, is that if one house is down, both houses likely would be down. Please correct me if I'm wrong, but I would think the most likely reason for the system to go down, assuming a leak-proof, pressure-checked, installation, would be a bad pump. That solution could be as simple as keeping 2 of each circulator/zone valve, one for backup if the corresponding operating unit fails.
Like maple1, I just can't see how to overcome this kind of head loss using small circulators and 1-1/4" or 1-1/2" logstor, much less 3/4" logstor. That's why I thought I'd need to break the install up into house 1 this year and house 2 next year. I guess I could possibly use larger circulators, but I was trying to use small ones if possible because I'm interested in minimizing power consumption in the event that I run the whole thing one day on solar.
As I understand, a reasonable estimate of head loss is:
Head loss = length of the longest loop * 1.5 (to account for resistance of fittings, HX's, bends in the pex, etc.) * 0.04 (all water with no glycol)
Head loss for house 1
560' * 1.5 * 0.04 = 34 feet of head (barn to highest and furthest points in house 1, and back to barn),
where 560' = [230' (GB to house 1) + 50' (distance from buried dualpex up into the attic and all the way over to the 17x20 and 20x20 WTAHX)]*2
Head loss for house 2
900' * 1.5 * 0.04 = 54 feet of head (GB to radiant supply manifolds, through any 300' loop, back to return manifold, and back to GB)
That is a rather large head loss for either circuit alone, much less combined:
34 + 54 = 88 feet of head
BTW, these head loss numbers seem to correlate with the Garn Design Manual. Referring to pages 13 and 14, a system designed with 20F dT's could flow hot water through 0.678" ID barrier pex (i.e. logstor 3/4") at 3GPM and 4.5GPM and deliver 30MBH (4 feet of head per 100') and 45MBH (6 feet of head per 100'), respectively.
At the 3GPM flow rate, a perfectly straight 560' pex pipe would see:
560' * (4FOH / 100') = 22.4 FOH
Similarly:
560' * (6FOH / 100') = 33.6 FOH
900' * (4FOH / 100') = 36 FOH
900' * (6FOH / 100') = 54 FOH
Add 50% of these values to themselves (the 1.5 figure in the calculations above) and you're in the same ballpark
As a side note, another reason I like your system description is that I don't plan to run glycol and the bypass allows for continual flow which would minimize any risk of lines freezing as long as there is no power outage. My planned LP backup generator for house 1 could provide that assurance because I'm running a 200 amp service from house 1 to the GB. The electrician can put all Garn and house 1 circulators, zone valves, etc. on that generator. House 2 already has a gasoline backup generator to do the same there.
Can you please provide some diagrams illustrating how a 3/4" system could be configured to do this?
I'm quite sure I wouldn't do series, and I would definitely not use 3/4" pipe underground.
For one thing - in the last diagram, the flow to house 2 is limited to what is flowing through the loads in house 1.
Although, I don't think we've seen the exact horizontal relationship between all three points of interest - barn, and two houses. One diagram showed the barn being between the two houses, houses being 230' & 300' in opposite directions (post 48 after looking back). Whereas the one in post 51 notes a 900' loop & 560' loop. I assume there is a triangle of sorts connecting the 3? Depending on that geometry, primary/secondary may even be a consideration.
the B+G NRF36 without a check valve is in that range using speed three and
reaching 34-35 feet of head pressure at 37 gallons per minute+-.
Yes, am putting a pressurized design together using 1-1/2" logstor for the primary loop as the head pressure appears to be half that of the 1-1/4". The Taco 2400 circs should be able to handle this high head situation presented by the long underground run. The head in the secondary loops should be able to be handled using circulators for those zones.A design such as yours, Antman, I find to be very challenging. I haven't added much input because I'm not sure I have the expertise to lead you to a satisfactory result. From my experience I do know that undersized pipe and long distances are major fundamental contributors to disappointment in or failure of installations.
A design such as yours, Antman, I find to be very challenging. I haven't added much input because I'm not sure I have the expertise to lead you to a satisfactory result. From my experience I do know that undersized pipe and long distances are major fundamental contributors to disappointment in or failure of installations.
I originally had planned to do that until I couldn't find high-flow manifold units with larger than 3/4" outlets. I haven't put that much thought in how to build one yet, because, up until recently, I have been trying to build an open system. It seems that pressurizing may solve several problems for me:Just get them in the house to a manifold as soon as possible (manifolds just inside the house).
If my secondary circs can better assist the primary circ, I guess a manifold serves me a lot more than the easier to build close tees. In building the manifold, is there anything in particular that lends itself to assisting the primary circ?But the secondary close T flows would not provide any assist for the main loops, whereas a manifold setup should.
you can certainly build it out of copper or black iron. you'll find out that black iron fittings are way cheaper than copper in the larger sizes.If my secondary circs can better assist the primary circ, I guess a manifold serves me a lot more than the easier to build close tees. In building the manifold, is there anything in particular that lends itself to assisting the primary circ?
thanks for following my thread, I appreciate your input. I think I'll put the exchangers in the GB so I can use a smaller, less-expensive circ on the open side (the Garn side) which will need to be stainless steelor you use a flat plate heat exchanger in the building (could be either the GB or house 1) and run the heating loops pressurized. (as a contractor this is what I would do, because if there are air problems in the floor loops, I have to go back and fix it and that costs the price of a heat exchanger the first time I have to go back.)
when you say smaller PEX, I'm assuming you mean for the secondary? I was planning on using a Taco bumble bee in set point mode with temperature sensor in the supply duct after forced air goes through WTAHXyou might find that you'll save $ by going with the smaller PEX, and running a high efficiency ECM circulator from wilo or grundfos. you'll have to do the math on that.
Read Dan's book pumping away and tried to further refine the schematic. Is there any reason why house 1 couldn't be pressurized and house 2 left unpressurized?So house 1 is getting 1-1/2 logstor but I still need to determine logstor size for house 2. I'll get around to running the headloss after kids go to bed but I'm hoping 1" logstor gets it done
I would like to know how to find the best WTAHX for my system (one with a wide delta T) but there doesn't seem to be a lot of options. I was considering Valutech but I was I haven't had a chance to call them to inquire about the design delta T for those units. I am under the impression from other threads that, in general, WTAHX have narrow delta T specs, like 10 or 15. Anyone know where to get 40? Stack 2 on top of each other?I'll just chime in and say that when it comes to pumping power required in a main circulating loop, there is no substitute for large bore pipe and tube.
The "entry fee" is higher initially but the dividend pays back forever.
The true system requirements will depend on the heat emitters more than anything else. (Think large and low temp with corresponding wide T.)
10GPM @ a 20* drop = about 100,000btu
5 GPM @ a 40* drop = the same.
Radiant floors, big radiators, oversized water x air heat exchangers, etc. These all allow less GPM to do the same "work".