I have been crunching numbers for my GARN primary/secondary setup. I am working toward finalizing the pump sizing for flow rate and head loss. In doing my calculations, I came across an interesting phenomena.
I have three loops coming off the primary; loop 1 with a 70k Btuh load, loop 2 with a 30k Btuh load, and loop 3 with a 35k Btuh load. Loop 1 is my house, loop 2 is a greenhouse (next highest temp) and loop three is my garage/workshop, which will have both forced air and radiant sources.
I decided to start with a 10GPM primary pump, as that gives me more than 60% of my total flow for the loops. I am starting with a water temp out of my GARN of 190 F, and using a delta T of 20 F. My water temps coming out of each loop are as follows:
Loop 1 - 176 F
Loop 2 - 170 F
Loop 3 - 163 F
Now, I decided to see what would happen with a 12 GPM flow rate. Here are the revised outflow temps:
Loop 1 - 178 F
Loop 2 - 170 F
Loop 3 - 163 F
Hmmm. No change downstream. Let me try 14GPM and see what happens to the outflow temps:
Loop 1 - 180 F
Loop 2 - 170 F
Loop 3 - 163 F
I have double checked my math, but it is apparent that when under full load, don't make a whole hell of a difference if I use a 10GPM pump or a 14 GPM pump.
Am I missing something?
I have three loops coming off the primary; loop 1 with a 70k Btuh load, loop 2 with a 30k Btuh load, and loop 3 with a 35k Btuh load. Loop 1 is my house, loop 2 is a greenhouse (next highest temp) and loop three is my garage/workshop, which will have both forced air and radiant sources.
I decided to start with a 10GPM primary pump, as that gives me more than 60% of my total flow for the loops. I am starting with a water temp out of my GARN of 190 F, and using a delta T of 20 F. My water temps coming out of each loop are as follows:
Loop 1 - 176 F
Loop 2 - 170 F
Loop 3 - 163 F
Now, I decided to see what would happen with a 12 GPM flow rate. Here are the revised outflow temps:
Loop 1 - 178 F
Loop 2 - 170 F
Loop 3 - 163 F
Hmmm. No change downstream. Let me try 14GPM and see what happens to the outflow temps:
Loop 1 - 180 F
Loop 2 - 170 F
Loop 3 - 163 F
I have double checked my math, but it is apparent that when under full load, don't make a whole hell of a difference if I use a 10GPM pump or a 14 GPM pump.
Am I missing something?