My system is set to hydraulic system 2 and working fine with buffer tanks.I saw that earlier...but with the buffer tank system, I do not see how anything other than #4 is an option.
My system is set to hydraulic system 2 and working fine with buffer tanks.I saw that earlier...but with the buffer tank system, I do not see how anything other than #4 is an option.
Im not so sure thats a good idea unless you know every setting of your system and what its set to. I think when you switch the type of hydraulic system when switched changes a bunch of other settings in the software.Well, I guess then, that is something to try. Thanks.
chew72, My tanks are about 72" tall and the top tank sensor is at about 58". All my sensors are in 1\2" wells. I purchased the tanks recommended by the supplier. Thanks for the "hysteresis" term. I will look around in the settings to see if I can find that. That is a big problem of mine is understanding what some of the terminology refers to. Thank you for your input.A quick question on storage tank sensor location. Is the top buffer tank sensor located a little way inside of the tank? I'm thinking between the top 5 - 10% of the tank. That's where mine is located and I have no issue. I'm thinking if it's located on the inlet pipe you may have greater heat loss and the temperature in the pipe is dropping a little lower than the buffer tank if there is no flow. Triggering the pump to come on.
I don't have a manual in front of me but if you wanted to increase the differential between turning on and turning off it would probably be referred to as a "hysteresis" value.
Mila70, I had a very hard time finding someone to even give me estimates. Heating companies in my area are busy and were not really looking to take on a job of this size. I did finally get 2 estimates. I had the S3 Turbo 50 installed with two 300 gallon tanks (used an existing Boiler mate) and all the recommended controls. I didn't want to cut any corners (which is why I am a little frustrated with my situation now). Both quotes were comparable for equipment. The installer that I chose came highly recommended and is a expert with solid fuels. The cost of just the equipment was about 23K. Piping and fittings and all other necessary equipment with the labor was about another 12K. If I could get to the bottom of the short cycling I would be very happy with the system also. I would say that the 600 gallons of storage would be minimum. I almost went with the 440 gallons and it would have been a stretch to make that work for me. I am heating about 3700 sq. ft. with a fairly tight construction. I hope this helps.Caiden, we're looking at installing a Froeling S3 Turbo with two 300 gallon tanks, but we're having some trouble figuring out how much it would cost us installed. Would you, by any chance, be willing to share a breakdown of your costs for the various components and materials, as well as the installation costs billed by your installer? I know that every system is different, but I think I'll be able to extrapolate since I have some sense (a list) of the various controls, valves, fittings, etc. planned. I'm just having a really hard time getting a straight answer, and the current estimate for the fully installed boiler and storage tanks and DHW with pump sensors, controls, fittings, valves, and piping is substantially higher than any estimates I've found online for a P4 installation with two 300 or even larger tanks and DHW and close to double what I've found for comparable systems with an S3 Turbo. I can't quite figure out why the numbers are so much higher except that the labor is a lump sum, and I have no sense of how much actual installation should cost. I would be incredibly grateful for any information!
That is interesting. I have 4 sensors as well and my installer put the all in the same tank. The tanks have 4 ports on the side and they are installed top, mid top, mid bottom and bottom. I wonder what the best is?All my sensors are in thermowells in the the tank....or tanks in my case as i have two.
And i have 4 sensors, 2 in each tank. These are located apprx 12" from top and 12" from bottom in each tank.
Yes if the sensors are just strapped on to an uninsulated pipe they will definitely see lower temperatures and not accurately measure the internal tank temperature. The sensors will also see a delay in this configuration.
I was able to catch the cycling. I have the pump to 25% minimum. When it is in "off" the pump comes on at 100%. If the temperature in the boiler or the top tank sensor stays the pump will run for 12 seconds then go to 25%. If either of the temps move to turn the pump off it will restart at 100% again.Im not so sure thats a good idea unless you know every setting of your system and what its set to. I think when you switch the type of hydraulic system when switched changes a bunch of other settings in the software.
I had the same short cycle time on my Froling. As the boiler cools after a burn the pump would kick on and off every few seconds for a long time. I could hear some water hammer in the pipes when it was happening.
I solved it by installing a time delay relay in the wiring for the pump. The relay will not turn off the power to the pump until it sees a prolonged off signal from the boiler. Every time the boiler tries to cycle the pump off then on again it resets the timer in the relay. The timer is adjustable. I think mine is set to wait 2 minutes. Its been 10 years this way with no issues.
Hello,
I have a question for fellow Froling users. I have a Froling S3 Turbo 50 with two 300 gallon storage tanks. I have been running it for about 3 months and love the system. I do have a concern that has been addressed with the supplier. When the boiler is in "Off" mode and the boiler is 4 degrees higher than the top buffer tank temp the circ pump starts. When the tank temp is 3 degrees lower than the boiler the pumps turns off. This temperature fluctuates often boiler up or tank down 1 degree causing the pump to continually cycle on and off sometimes several time per minute. This does not seem to be good for the pump. Shouldn't there be a buffer when the pump cycles on it should remain on for a certain amount of time? Has anyone experienced this issue? If so is there a fix? If not a fix does anyone agree with the supplier that this is "the nature of the beast". Any comments or suggestions would be greatly appreciated. Thanks
I did not read the full write up here, but unless you have a variable speed pump controlled via 0-10V signal from your Froling boiler the speed setting will NOT do anything for you.
It sounds to me that you need to setup a wider differential band.
I'm only familiar with Windhager.
Is there a higher level available? SERVIVE level or level for the Froling technician?
You will probably need an access code, or a combination of push buttons to hold at the same time
I self-installed an S3 Turbo with the 3200 controller. It came with old firmware so I updated it to 50.04_5.20 (the latest) and it does not short cycle. The English docs posted on the Froling site for this version are much better, especially after I figured out that releasing a pump means turning it on. Which firmware are you running?We have walked through all settings on the manual with our local support and cannot find any parameter really controlling the pump at standby mode. The pump minimum & maximum speed settings do apply for this 0-10V speed controlled pump in heating mode. In standby the max pump speed seems to apply but the pump never enters minimum speed, instead it turns off completely (might use min speed if the buffer tank and the boiler were colder than ever in normal operation). In any case, these settings do not prevent the short cycling even with the speed controlled circulation pump (for which the settings really are for).
I self-installed an S3 Turbo with the 3200 controller. It came with old firmware so I updated it to 50.04_5.20 (the latest) and it does not short cycle. The English docs posted on the Froling site for this version are much better, especially after I figured out that releasing a pump means turning it on. Which firmware are you running?
The primary circ is a 0-10V controlled ECM unit from Resideo connected to the hydraulic module. The system is configured as System 4 with 4 storage temp sensors. Boiler protection is provided by a thermostatic mixing valve. I do have the return sensor connected but I haven't seen any way to read it so I'm not sure it's being used. The boiler adjusts the circ speed and burn rate to hold a delta-T of about 20F. The minimum buffer tank pump speed is set to maybe 20%, I'd have to check for sure. I think I set 'mid buffer controller active' to yes. I also set the correct buffer tank volume.
Once all the wood is consumed, the primary circ turns off, the residual heat increases the boiler temp and the circ is run briefly to drop the boiler temp. This might happen twice then it stays off until fired again. I just posted a response to another thread with a plot showing this behavior along with a description of the plot:
https://www.hearth.com/talk/threads/a-question-ive-never-been-able-to-answer.207323/post-2766597
I have seen the circ run once with the boiler in standby but this was probably the pump stall protection which will run the circ for 15 secs at 100% on some unspecified periodic schedule.
From the way-back department, someone reported that the P2 does not like low-energy pumps. I'm not sure which controller is in the P2 but the +valve option might change your system behavior:▪ Field pump / PDM <- you would want 0-10V mode instead of PDM, this is your current setting since the 230V stays on all the time
There is a permanent power supply of 230V at the output for the high efficiency pump. The pump is controlled using
pulse duration modulation at the respective PDM output.
▪ Field pump PDM +valve <- you would want 0-10V mode instead of PDM
The signal for the field pump is emitted at the PDM output. If the signal exceeds 2%, the 230V output is switched on. If
the signal is below 2% for more than 4 minutes, the output is switched off again.
This does not seem right to me but I may not understand exactly what you are saying. The controller should try and keep some delta-T from the boiler supply to return (settings on page 65?) when it's heating. With my external sensors, I see about 20F / 10C delta when the pump is running and the boiler is heating. The boiler protection valve is an LK823 with 65C element. It opens a little to mix in some colder water from the bottom of storage but does not open fully until storage is almost 100% charged. Once the wood is consumed, the boiler supply temp from the boiler display will increase to about 190F then the pump runs briefly to pull this back to 185F a few times. The return temp is held fairly constant, I think. My plots for supply, return and delta-T are not correct since the sensors are external and only accurate when there is water flow. I suppose what you are seeing makes sense - if the boiler temp does not exceed the target, there is no need to run the pump and open the mixer so the supply and return would stay close to the same temp.at the start of standby mode, the lower buffer temperature is less than 70 degrees while the boiler temperature is in the 81 to 82 degrees range. However the boiler does not open the mixer and run the pump properly but instead keeps the return temperature very close to the boiler temperature.
The mixer appears to go back to full bypass (no storage return) when in standby. This would mean that even though there is 70C water at the bottom of storage, the boiler return will not see it immediately. The pump must run then the mixer must open then the water must flow to the sensor (dependency on pipe length & sensor location) before the return measurement is valid. The return temp should be ignored until this has happened. If this time is too short, the controller might decide that "I turned on the pump, immediately checked the temps, there was no difference in boiler output and return so running the pump had no effect, turn off the pump, the boiler output is still too high, try the loop again." If this is the case, it seems like it would repeat until the boiler dissipates some heat and the short cycle behavior ends after a few hours. Your observation that the boiler temp drops below the top of the buffer temp and the short cycling stops around the same time makes sense if this is the case.Waiting time for calculating the return temperature setpoint adjustment. Once the specified time has passed, the heating system temperatures are evaluated.