While i agree that code are a minimum and we regularly exceed them the minimum thickness of a connector pipe is 24 gauge. I would agree that stainless would be better but it still needs to meet that minimum thickness. As far as 304 versus 400 series. all of the commercially available stainless connector pipes are 400 series and they last a long time i see absolutely no problem with it and they will last much longer than that light wall liner which can and will eventually burn through. Also there is nothing in any code allowing for a flexible connector pipe it simply is not there and his claim that is will flow better is just wrong the corrugated pipe reduces flow more that a couple low angle elbows with smooth pipe would. The projection past the wall is a requirement of the liner manufacturer and any i have worked with require 1.5" I don't know what brand he used but I have never come across one that required less than that. And following manufacturers instructions is a code requirement