Doityourself said:
Hello,
I am not sure if I am understanding correctly. After re-reading my post, I relized that I was not clear on which mixing valve I was talking about. I am running full temperature (180-200) though my in floor heat, no mixing valve. I am interested in sizing the mixing valve for the return water so that my temperatures aren't too cold coming back from the heat load.
Right, you could have a mixing valve to set the temperature supplied to the floor, and you could have a mixer to set the temperature of the return temperature to the boiler. (Or none, or both.)
If a system has a mixer for controlling return temperature, it is usually set up such that a boiler circ pump pulls water through the mixer into the return port of the boiler. The mixer in turn is set up such that it can pull water from the supply outlet of the boiler and/or from the return side of the load.
I'm saying that in order to flow enough water to pull full capacity out of a typical boiler, such a valve needs to be comfortably free-flowing. But then again depending on the delta-T through the boiler and how much capacity you really need, it's possible a smallish mixer might do the trick, but you'd need to get a handle on the critical parameters and do the arithmetic in order to have any confidence in going that route.
I am thinking that since I am running full temperature to the floor, I may not have an issue with return temperatures being too low just because I am running a high temperature out. So far I have been running this a week, lows in the 20s highs in the 50s which is still pretty warm for central WI. I do not circulate water below 180, the pump is hooked to the aquastat to ensure that the boiler is up to temperature so I don't have creosote problems. The blower for the induction is on up to 200, then the pump turns on down to 180, then the fan kick in and the pump turns off.
Thanks!
I believe typically combustion control and circ control are two independent functions.
Circ pump: If demand is calling and boiler temperature is high enough (e.g., greater than 160F), the circ runs. If no demand or boiler temp too low (e.g., 150) the circ shuts off.
Combustion air: If demand is calling control combustion air to achieve supply temperature setpoint (e.g., 195F). If no demand suppress combustion, but maintain minimum boiler temperature (e.g., 160F).
I would be concerned about leaving the circ off all the way up to 200F; hot spots, stress, warpage, flashing, stuff like that. (Not to mention dust, bacteria, and aldehydes of afraidium.) YMMV.
Cheers --ewd