Hi plips.I just installed a Tundra in my home and I'm having the same problem. Black liquid coming out of the elbow that slopes upward towards my chimney. The chimney is about 25 foot tall and has 9x9 clay tile inside. It does not yet have a liner and I haven't installed my barometric damper yet but will be soon. The wood is good and thought I had enough makeup air but might add more. I let the fire get rolling before closing the damper and I do notice the flue pipe temps drop enough that I can put my hand on it. Should I just leave the damper open? Was going to hook it up to a t-stat tonight but I might wait until I get the damper. We have a stack of Dwyer Mark 2 type 25's at work, I'll snag one and get some hard line and install it, should it go before the barometric damper? Thanks all.
First of all, how many fires have you had in it...it can take a couple good fires to dry out the firebrick it seems.
Second, how dry is the wood...that's always the number one suspect.
Third, you need some type of thermometer to get a flue temp reading...you may not be getting things hot enough before the damper shuts.
Forth, a 9x9 clay tile chimney has a very low chance of working out for you IMO. The cross section area of that chimney is 63.5 sq. inches, Drolet calls for just over 28...so you are over double. These things just don't waste enough heat up the flue to keep that much area warm enough to work. Plus a square flue doesn't flow as well as a round one. The good news is 9 x 9 is a good size to be able to drop an insulated liner in.
And yes, the draft sample needs to be taken between the baro and the stove