Hi all.
I had my first fire(a small one) with mixed results yesterday. Had pressure tested my system upto 30psi and it held. (Could not test any higher because of the pressure relief valve). Feeling confident, I filled the system with water, and it held - no leaks. Ran the circ for a while with just cold water, also no leaks.
Started up the fire and it ran about 2 hours and I had a blowout (one of the soldered joints developed a leak) in one of my copper lines - quite a mess, (in the cellar at least). Have spent the last 24 hours (except for sleep), draining the lines, and re-pressure testing this time upto 45 psi this time (i took out the releif valve).
Question is, as of right now I am holding steady at 45PSI(with air), the system should never exceed 30PSI when its running, and in fact yesterday when I was doing a test burn never got above about 18psi, so why did my joint fail? Now I am nervous about firing it up again.
My past experience with plumbing (not heating systems though) has always been, if it doesn't leak right away, it never does...but in this case, as the circulating water got up to about 160 it failed.
Did the high temperatures cause this failure of a marginal joint? Before I re-fill and re-start the fire, any other advice?
I had my first fire(a small one) with mixed results yesterday. Had pressure tested my system upto 30psi and it held. (Could not test any higher because of the pressure relief valve). Feeling confident, I filled the system with water, and it held - no leaks. Ran the circ for a while with just cold water, also no leaks.
Started up the fire and it ran about 2 hours and I had a blowout (one of the soldered joints developed a leak) in one of my copper lines - quite a mess, (in the cellar at least). Have spent the last 24 hours (except for sleep), draining the lines, and re-pressure testing this time upto 45 psi this time (i took out the releif valve).
Question is, as of right now I am holding steady at 45PSI(with air), the system should never exceed 30PSI when its running, and in fact yesterday when I was doing a test burn never got above about 18psi, so why did my joint fail? Now I am nervous about firing it up again.
My past experience with plumbing (not heating systems though) has always been, if it doesn't leak right away, it never does...but in this case, as the circulating water got up to about 160 it failed.
Did the high temperatures cause this failure of a marginal joint? Before I re-fill and re-start the fire, any other advice?