Jim K, you're probably right about letting air out. It has not gotten much better.
mpilihp, my storage tank is 500 gallons, my extrol exp. tank, on my wood boiler, is 7.6 gallons according to Amtrol's site. The expansion tank on my gas boiler/house loop is about half the size of the Amtrol 60.
BoilerMan, the 5% rough calculation (considering 500 gallons storage, plus 50 gallons piping, etc.) is putting me in the 27.5 gallons area. WOW! I suppose my kids don't need to go to college. LOL.
BenW, My current T/P valve on the gas boiler says 30# and 535,000 btus an hour. So the fact that the pressure was so high, that is what caused it to blow off originally. I will have to replace it because of the continual leaking.
To all, I have not resupplied the exp tank with any air yet. My system temps and pressure are as follows....My Eburn shows 172 deg and 32 lbs and my gas boiler shows 160 deg and 22 lbs. Both readings are from the mechanical gauges on the internal tanks. Why would it show more poundage (sp?) on the wood boiler? Should it not show a lesser pressure? The wood boiler is 1 floor above the gas boiler. It is also about 100' away in the unattached garage....hmmm..very weird. The gas boiler T/P valve is still seaping very slowly....no doubt from overuse at this point. At least it's not peeing on the floor any more. It evaps before it makes it to the floor.
I will put another Extrol 60 on this spring's budget and pipe it in series with the other...should I also include another air scoop and air vent with the second one? If not, should it be before or after the existing one? I will replace the gas boiler T/P valve.
If any of you are familiar with my system, the 1" pex lines ARE too small for my application. I will have to run 2 additional 1" lines or replace the lines with 1.25 or 1.5 inch lines in the spring. I'm going to limp through this winter as is. It really sucks and I'd better not cross paths with the dope that spec'd the 1" pex
!! I've blown about $1000 dollars making this stuff work and it isn't quite cutting it. What does everyone think of putting a second Taco 007 on the return line on the gas boiler end to (pardon the expression) 'push' the return water back to the wood boiler? I currently run the other Taco 007 24/7 to keep the ground lines from freezing and another 007 running isn't going to kill my electric bill and should improve the flow through the 1" pex. ???? Thoughts?
I appreciate all of the info you have give and any more thoughts would also be appreciated.