Getting back to air sealing...I am, by nature, curious and I want to know how "tight" my house is and whether I should pursue more air-sealing measures. I want to stop short of adding a ventilation system (I don't want to make it too tight) due to cost and the fact that I have hydronic heat, so adding extra ventilation would be somewhat problematic and expensive. Here is the short summary (detail below) - I've tightened up a lot and achieved good results (the blower-door test guy was amazed at what I've achieved in my old house), but I still have room to improve (if I want to). It's almost impossible to make an old house too tight without a gut rehab.
Details:
I knew my CFM50 (and therefore my ACH50) and I had been wondering what the best "conversion" from ACH50 to ACH natural (not pressurized) should be. I had heard from elsewhere that a divide by 10 was a pretty good number to use, and others here (Woodgeek, Dick, Gary) suggested numbers in the range of 12-20. I used Gary's adjustment calculator (seep previous post) and came up with 16.375.
I also found that this presentation link
http://www.buildingscienceconsulting.com/presentations/documents/Expert 2013 - Ventilation_rev.pdf confirms this range of numbers. See page (not slide) 62 and look at the slide in the bottom right where it references a study of a home in Quebec City that compared the ACH50 to a gas tracer test reading at normal pressure. The ratio was 4.16 (ACH50) / .30 (average gas tracer reading), or about 14.
So, I am going to assume 15 for my conversion from ACH50 to ACH(natural).
My original house blower door test was 1800 CFM at 50 Pa. I was told that if I sealed up the attic hatch better and the basement access door (which I subsequently did), I would probably drop to around 1200 CFM at 50 Pa, so I am going to use 1200 CFM as my "test" value. My house is 1250 square feet with a full basement, and 8.33 foot high ceilings in the living area and 7.5 foot height in the basement. So that gives me about 19,750 cubic feet. My ACH50 is (1200 cubic feet/minute * 60 minutes/hour) / 19,750 cubic feet = 3.65. My ACH(natural) would then be 3.65 / 15 (from above), or 0.24. I'm feeling pretty good about this, especially since my house is a 1922 bungalow, and I still really need to get into that attic and seal up a few hard to reach ceiling penetrations....Essentially, ACH50 of 3.0 is what you can get if you seal up the big holes and a 1.5 is possible addressing smaller holes (per the link above). I'm nearly there.
Now, I'd like to know "what is the lowest I could go without creating "problems" (health, odors, moisture, etc.) or without requiring mechanical ventilation. My "gut" tells me that I can push a little further...
Using my 0.24 ACH(natural), that would mean 86 CFM for the house, or doing the math (0.24 air changes/hour * 19,750 cubic feet) / (60 minutes/hour) = 79 cubic feet/minute of natural ventilation.
Referencing the above Joe Lstiburek presentation, the desired CFM for the house is 7.5 CFM per person + 0.01 to 0.03 CFM per square foot of conditioned living space. "Person" is defined as numbers of bedrooms + 1, which would mean 4 (even though my wife and I are the only occupants of the house). So that means 4 * 7.5 CFM + 0.01 * 1250 (square footage of living area) = 42.5 CFM (using the BSC formula) or 67.5 CFM (using the ASHRAE formula with a .03 multiplier). See pages 63 and 67 of the above referenced link for these formulas.
So it looks like that I am in the "safe" zone still on not making my house too tight. This is not surprising given that it is really, really hard to make an old house too tight unless you do a gut rehab (which there is no need to do on this house).
Next up...I need to motivate myself to rip up the attic floorboards and seal a few pesky ceiling penetrations, and also seal around the chimney chase. I can also make a few more improvements to the basement door sealing - realistically, I am probably not getting all the improvement I should since there are some areas I didn't seal at all and now that winter is here, I can feel the result of this.
Those planning to achieve the results I have should note that I have no appliances (excepting my wood stove) that utilize house air for combustion. Summary below:
Stove - electric
Range - electric
Water Heater - heat pump with electric backup
Boiler - oil using outside combustion air (though not "sealed combustion")
Woodstove - uses inside air for combustion drawn from the basement
I absolutely did not take the final steps to seal up the basement doors really well until I had a new boiler installed that used outside combustion air. I had previously noticed that if I was trying to establish a new fire and run the boiler at the same time, my woodstove chimney draft wasn't as good as it was with the old oil boiler not running. This raised concerns about sufficient ventilation to run these two appliances simultaneously. Now, there are no problems if I run both simultaneously.