I'm on a budget here...
(broken link removed to http://video.google.com/videoplay?docid=1569125216323959688#)
(broken link removed to http://video.google.com/videoplay?docid=1569125216323959688#)
oilhater said:I have a 5500 watt generator. Back fed through the dryer outlet.......
Agreed 100%macman said:oilhater said:I have a 5500 watt generator. Back fed through the dryer outlet.......
Aren't you afraid of backfeeding through the incoming feed lines, and possibly electrocuting a power company lineman trying to fix the power outage?
Not saying that you aren't being careful, but mistakes do happen. Why not just do it the right way and install a manual transfer switch?
oilhater said:.....I agree, the transfer switch is the safest way to go...but i'll bet of all the people w/ generators out there, only a small % are done that way.
oilhater said:That's why you shut the main off before you start the generator. I'd rather do it this way than using extension cords hacked into boiler switch's or outlets. I agree, the transfer switch is the safest way to go...but i'll bet of all the people w/ generators out there, only a small % are done that way.
tkrock said:oilhater said:That's why you shut the main off before you start the generator. I'd rather do it this way than using extension cords hacked into boiler switch's or outlets. I agree, the transfer switch is the safest way to go...but i'll bet of all the people w/ generators out there, only a small % are done that way.
I do it exactly this way at my house too. BTW, the guy on the pole isn't going to get shocked. If that were the case you'd be powering the whole block and the generator would turn off anyway because it couldn't handle the load because you'd be powering everyones pellet stove. The bigger reason to turn off the main is so when the main comes back on the rest of the house doesn't get double the voltage and more likely the generator itself gets cooked.
BrotherBart said:tkrock said:oilhater said:That's why you shut the main off before you start the generator. I'd rather do it this way than using extension cords hacked into boiler switch's or outlets. I agree, the transfer switch is the safest way to go...but i'll bet of all the people w/ generators out there, only a small % are done that way.
I do it exactly this way at my house too. BTW, the guy on the pole isn't going to get shocked. If that were the case you'd be powering the whole block and the generator would turn off anyway because it couldn't handle the load because you'd be powering everyones pellet stove. The bigger reason to turn off the main is so when the main comes back on the rest of the house doesn't get double the voltage and more likely the generator itself gets cooked.
Well, let's not forget here that it is against the law in all 50 states to do what you are doing.
mnkywrnch said:http://www.northerntool.com/webapp/wcs/stores/servlet/product_6970_200196674_200196674
This is what I bought for the money its not bad,and a friend who's a licensed electrician installed it for me.
That's what I have. One of the best investments I've made. No worries during power outages, and it increased the value of my home.Sheepdog said:....when I have the cash, I will upgrade to an auto-standby whole house generator, and run it off propane......
maineheat said:I currently don't have a generator, but I'll probably get a cheap portable and do the following:
1. Add a Main Panel generator interlock which prevents the generator inlet to be powered if the main breaker is on
http://www.interlockkit.com/
2. Add an outside power inlet
3. Let it rip!
This seems a lot cheaper than a transfer switch, seems like easy to install, gives you the flexibility to turn on the breakers you want in your panel, and covers you behind as far as UL and not back feeding to the grid. You could probably get away with cutting a piece of metal stock to avoid paying $150, but then again it's not UL.
tkrock said:oilhater said:That's why you shut the main off before you start the generator. I'd rather do it this way than using extension cords hacked into boiler switch's or outlets. I agree, the transfer switch is the safest way to go...but i'll bet of all the people w/ generators out there, only a small % are done that way.
I do it exactly this way at my house too. BTW, the guy on the pole isn't going to get shocked. If that were the case you'd be powering the whole block and the generator would turn off anyway because it couldn't handle the load because you'd be powering everyones pellet stove. The bigger reason to turn off the main is so when the main comes back on the rest of the house doesn't get double the voltage and more likely the generator itself gets cooked.
Groundhog said:maineheat said:I currently don't have a generator, but I'll probably get a cheap portable and do the following:
1. Add a Main Panel generator interlock which prevents the generator inlet to be powered if the main breaker is on
http://www.interlockkit.com/
2. Add an outside power inlet
3. Let it rip!
This seems a lot cheaper than a transfer switch, seems like easy to install, gives you the flexibility to turn on the breakers you want in your panel, and covers you behind as far as UL and not back feeding to the grid. You could probably get away with cutting a piece of metal stock to avoid paying $150, but then again it's not UL.