did you ever find the right amount of blockage - curious how much that was
Yeah so I think I've settled in on 1/4 inch inlets into the secondaries which equals approx 60% reduction overall. Seems like a lot but the stove behaves so much better now. The primary air control actually has a meaningful impact at different settings now versus before it was basically just open/closed.
Even with a say 50% reduction I was still running into over-firing issues on a full load. The flue connector area temps would still climb to 900+ and glow a little bit. Now I can load it up full, close it down, get beautiful secondary action and just cruise and ~850 degrees at the flue connector area and nothings glowing.
Oh, and I'm noticing that the white ash film that would accumulate on the glass after a couple hot fires is gone. Someone in another thread mentioned that this was caused by excessive draft but I didn't believe it because everything I've read basically says I'm just barely situated for acceptable draft.
With a 17ft chimney and not incredibly cold environment there is no reason for me to believe that I have too much draft but I don't know how else to explain it. The stove was an absolute blast furnace before the mod. Now it's tame and controllable. Sure it takes a little bit more finesse to dial it in and not kill the fire when shutting the air down but as I understand that's the way these stoves are supposed to work.