System is plumbed as shown below - storage tank not online. Thanks for all the help and comments.
Controller board not installed.
Looking to finish failsafe mode before controller is added.
All circulator (C-1 through C-5) are Grundfos 15-58 with internal flow checks. All are set to low speed.
All zone valves are Honeywell 3/4" normally closed except the one from the Seton to the storage tank.
Failsafe mode definition - mode that system runs in if computer controller fails.
Failsafe issue is the C-5 circulator pulling through the AM-102R mixing valve - set at position 13 - about 125F.
If there is a heat source on - right now only the Seton, then everything is fine. If the Seton circulator is off (set by Seton aquastat on Seton supply at 145F) then the mixing circulator C-5 continues to run and will pull hot (or cold) water through any of the heat sources. The propane boiler happens to be the shortest route and I have a cutoff to prevent flow through it now.
So, my options as I see it are:
1. Only allow the mixing circulator (C-5) to run if one of the other circulator are on.
2. Place aquastat on main supply and shutoff C-5 if the temp falls below a threshold - allows for heat scavenging.
3. Place zone valve on each heat source to prevent flows when not operating.
So, for failsafe (no computer controller), what would you suggest for controlling C-5.
I guess this is similar issue to a primary/secondary system when the primary loop circulator is off?
Thanks,
Steve
Controller board not installed.
Looking to finish failsafe mode before controller is added.
All circulator (C-1 through C-5) are Grundfos 15-58 with internal flow checks. All are set to low speed.
All zone valves are Honeywell 3/4" normally closed except the one from the Seton to the storage tank.
Failsafe mode definition - mode that system runs in if computer controller fails.
Failsafe issue is the C-5 circulator pulling through the AM-102R mixing valve - set at position 13 - about 125F.
If there is a heat source on - right now only the Seton, then everything is fine. If the Seton circulator is off (set by Seton aquastat on Seton supply at 145F) then the mixing circulator C-5 continues to run and will pull hot (or cold) water through any of the heat sources. The propane boiler happens to be the shortest route and I have a cutoff to prevent flow through it now.
So, my options as I see it are:
1. Only allow the mixing circulator (C-5) to run if one of the other circulator are on.
2. Place aquastat on main supply and shutoff C-5 if the temp falls below a threshold - allows for heat scavenging.
3. Place zone valve on each heat source to prevent flows when not operating.
So, for failsafe (no computer controller), what would you suggest for controlling C-5.
I guess this is similar issue to a primary/secondary system when the primary loop circulator is off?
Thanks,
Steve