That may be an error, examples?Many stove manuals say 18" to the CENTER of the pipe for single wall.
That may be an error, examples?Many stove manuals say 18" to the CENTER of the pipe for single wall.
But appliance manufacturers can test for clearance from single wall pipe for their appliance. They do it all the time for furnaces and they are just ul listed appliances just like wood stoves. And like woodstoves the default is 18" for singlewall unless specified otherwise.It is a bs manual and response. Uncertified single wall pipe needs 18"s of clearance. If they tested it and certified it it would have a certification sticker on the pipe. Just because they tested their stove at those clearances, doesn't mean that the testing cert extends to uncertified single wall pipe. So unless they supplied certified single wall with their stove, with a certification decal on it showing reduced clearances. The single wall pipe that you buy to hook up their stove is still uncertified and requires 18" of clearance.
Well in canada it is pretty clear but usa it is not. Like i have said because it is a grey area i go with 18" but as far as i can tell by code an appliance manufacturer can reduce clearancesCan you find any others? I'm confident there are some. It is a manufacturer oversight IMO.
B365 - 4.2.1 Manufacturer’s certified instructions
Certified appliances, accessories, components, and equipment shall be installed in accordance with the
manufacturer’s certified instructions. When a difference exists between the manufacturer’s certified
instructions and the requirements of this Code, the manufacturer’s instructions shall take precedence.
Note: A flue pipe is not considered a component of a certified appliance (see note to Clause 6.4.7).
B365 - 6.4.7
The minimum clearance for a flue pipe adjacent to a combustible surface shall be 450 mm (18 in),
regardless of whether the surface is covered with noncombustible material such as plaster or cement
board. See Figures 3 to 5.
Note: The flue pipe clearances shown on wood stove certification labels are for information purposes only and do not supersede the clearance requirements of this Clause.
In Canada there is no question about this. Ulc s627 is our standard and it is an appliance testing standard, not a flue pipe testing standard. To try to blur the lines of appliance certification to potentially compromise safety is foolish.ymmv in the USA, but I would never recommend installing a single wall flue pipe closer than 18"s to combustibles.
Can you find any others? I'm confident there are some. It is a manufacturer oversight IMO.
Note: The flue pipe clearances shown on wood stove certification labels are for information purposes only and do not supersede the clearance requirements of this Clause..
Well in canada it is pretty clear but usa it is not. Like i have said because it is a grey area i go with 18" but as far as i can tell by code an appliance manufacturer can reduce clearances
Some regency stoves doOther stove manuals that show reduced clearances for single wall pipe. For me, because I'm interested in the information.
Yeah i know and i have yet to get a good answer from any manufacturer on that yet.I'll throw this can of worms out there.
So where a single wall pipe meets a certified ceiling support box, just how close does that single wall get to combustibles? Well under 18"s and right at the ceiling too, near horizontal surfaces instead of the 18"s required all the way up near vertical surfaces.
Agreed, the most conservative clearance requirement should be honored.I have no real experience/knowledge in that regards. But for stoves this same issue has been discussed at length on another forum I'm a member of and in Canada I'd feel confident in saying that the 18" clearance for single wall should be honoured.
For one it would be none other than the Quad 3100 MilleniumView attachment 227666 View attachment 227667 . Shown as 18.25" to the center.
You are right, the popular F2400 does this too. What does a Regency installer do in this circumstance with a single-wall stove pipe installation? Follow Regency's manual or Ventis's explicit instructions? It would seem that violating the stove pipe mfg. directions would void the pipe warranty and place liability on the installer if any issues arose.Some regency stoves do
I'll throw this can of worms out there.
So where a single wall pipe meets a certified ceiling support box, just how close does that single wall get to combustibles? Well under 18"s and right at the ceiling too, near horizontal surfaces instead of the 18"s required all the way up near vertical surfaces.
Agreed, the most conservative clearance requirement should be honored.
Very interesting, That's from the same HHT documentation dept.. They need a review of stove pipe specs. Here is the original Quad Millenium 3100 doc diagram. Note the clearance A.
View attachment 227668
You are right, the popular F2400 does this too. What does a Regency installer do in this circumstance with a single-wall stove pipe installation? Follow Regency's manual or Ventis's explicit instructions? It would seem that violating the stove pipe mfg. directions would void the pipe warranty and place liability on the installer if any issues arose.
Like i said personally i use double wall. But due to the fact that the pipe is unlisted and is not tested for clearances. While regency assures me their clearances are all tested and verified. It should be safe and to code to follow regencies clearances. Because code only references listed product instrucions to be followed.You are right, the popular F2400 does this too. What does a Regency installer do in this circumstance with a single-wall stove pipe installation? Follow Regency's manual or Ventis's explicit instructions? It would seem that violating the stove pipe mfg. directions would void the pipe warranty and place liability on the installer if any issues arose.
That is dang good warranty. Not sure what clearance has to do with rusting away but OK. I guess they could use that against you but how would they know how close it was?Olympia (Ventis) has a 10 yr warranty on their single wall.
If there was a fire or even a scorched wall claim.That is dang good warranty. Not sure what clearance has to do with rusting away but OK. I guess they could use that against you but how would they know how close it was?
And as far as liability goes the installer is always the lowest guy on the totem pole. It all fall on us. Which is why i never install stoves or connector pipe to minimum. I always allow atleast an extra inch.You are right, the popular F2400 does this too. What does a Regency installer do in this circumstance with a single-wall stove pipe installation? Follow Regency's manual or Ventis's explicit instructions? It would seem that violating the stove pipe mfg. directions would void the pipe warranty and place liability on the installer if any issues arose.
Yes but fire or scorching has nothing to do with the warrantyIf there was a fire or even a scorched wall claim.
Ventis's warranty on their double-wall stove pipe is forever, even if the house is sold.
Agreed. So in this case is that an extra inch over the stove clearance spec or the stove pipe clearance spec? For me, it would be the latter.And as far as liability goes the installer is always the lowest guy on the totem pole. It all fall on us. Which is why i never install stoves or connector pipe to minimum. I always allow atleast an extra inch.