I am surprised to see that you aren't interested in digital readouts on CO detectors. Myself I want to know if there is ANY CO present and I will investigate as to why. Here is the industry standard on how an detector will go into alarm.
After Oct. 1, 1998, UL 2034 listed CO alarms must measure and alarm when CO is:
30 PPM for 30 days
70 PPM for no more than 240 minutes before alarming (may alarm as early as 60 min.)
150 PPM for no more than 50 minutes before alarming (may alarm as early as 10 min.)
400 PPM for no more than 15 minutes before alarming (may alarm as early as 4 min.) and have a manual reset that will reenergize the alarm signal within 6 minutes if the CO concentration remains at 70 PPM or greater.
From this article.
(broken link removed)
Generally . . . what I have found on the job and in my home . . . if the CO alarm is going off there is CO somewhere. On the very few occasions it has gone off in my home I was able to quickly determine the source of the CO and fix the problem (latest incident simply involved me opening the garage doors and not lingering in the breezeway with the door to the garage open). If there was any question in my mind as to the source or if anyone was exhibiting some signs of CO poisoning I would not hesitate to call up the FD to get a CO monitor.
That said, there is absolutely nothing wrong with wanting to know the CO levels . . . especially if it gives someone a peace of mind . . . and I could see it being useful when calling the FD to be able to tell them the levels are at X ppm.