Hi all,
I've been asked to help my neighbor work out an install of his new Aquatherm OWB. My own system is much simpler so I had a lot of reading to do to get up to speed.
He's run the underground pex as one continuous series from Boiler > House ( sidearm > main furnace > sidearm > workshop furnace ) then 200' underground to a new 700 sf outbuilding w/ in-floor hydronic > return to boiler. With fittings losses etc I figure his 1" equivalent length is 750' total.
Best guess on max demand is 230,000 BTU. Assuming 180* out, 110* return ( dt = 70* ) I need 7 GPM.
This will take 2 high-head pumps like the Grundfos UP 26-99 I ordered.
I figure for 80 or 90% of the heating season he could probably run on 150,000 BTU or less, which means <5 GPM which I can get with one pump running.
My thought to save electricity is this.... run the main circ on the boiler continuously. Inside the basement mid-way through the system put the second circ, but trigger it to run only when the main furnace fan is running ( simply tap off the furnace blower power supply ). This would bump my flow from 5 to 7 GPM only at the times his main heat load is demanding.
How much headloss is there to pump thru a un-powered pump? Is there a problem with doing this that I am not anticipating?
Is a return temp of 110* a system killer? ( his last load is the hydronic side loop so it should function that cold, no? )
I've been asked to help my neighbor work out an install of his new Aquatherm OWB. My own system is much simpler so I had a lot of reading to do to get up to speed.
He's run the underground pex as one continuous series from Boiler > House ( sidearm > main furnace > sidearm > workshop furnace ) then 200' underground to a new 700 sf outbuilding w/ in-floor hydronic > return to boiler. With fittings losses etc I figure his 1" equivalent length is 750' total.
Best guess on max demand is 230,000 BTU. Assuming 180* out, 110* return ( dt = 70* ) I need 7 GPM.
This will take 2 high-head pumps like the Grundfos UP 26-99 I ordered.
I figure for 80 or 90% of the heating season he could probably run on 150,000 BTU or less, which means <5 GPM which I can get with one pump running.
My thought to save electricity is this.... run the main circ on the boiler continuously. Inside the basement mid-way through the system put the second circ, but trigger it to run only when the main furnace fan is running ( simply tap off the furnace blower power supply ). This would bump my flow from 5 to 7 GPM only at the times his main heat load is demanding.
How much headloss is there to pump thru a un-powered pump? Is there a problem with doing this that I am not anticipating?
Is a return temp of 110* a system killer? ( his last load is the hydronic side loop so it should function that cold, no? )