Found a tube of "siliconized" concrete crack sealer I bought not too long ago. Wonder if that'd be as good as pure RTV ?
Sikaflex makes good stuff. We used their products extensively when building boats. Sikaflex 1a should work well. FWIW, I have had very good results using GE Silicone II over the years on several projects. It has good adhesion and stands up well. There is no need for RTV in this application.V1 can be acidic, V2 uses alcohol for curing and is non acidic but more expensive. I am fan of the Sikaflex line of polyurethane sealants, many will take paint, silicone does not.
I tried a caulk made specifically for masonry, and it was a friggin' mess. Think of Quad caulk, but if it was already half-cured coming out of the tube. Not sure if I just got a bad batch, it was well-within the expiration date, but it was the worst stuff I've ever used.There's caulk meant for concrete, tempted to use it.
I'm talking about block wall penetrations (minisplit lineset, subpanel, central vac, outdoor outlet for radon fan) so this has nothing to do with the catwalk. For the concrete, I bought Sikaflex 1a which people (above) seem to think will be perfect.sorry i'm late to the dance. geo has it going tho. i use ge 2 caulking also it does stand up to time. i wouldn't cheap out with that stuff because it will be moving. sun, wind, people walking along the walkway.
Well, I've already bought the THWN and a lot of the conduit fittings, so ...it's to bad i wasn't here earlier i'd say use ser cable and you are done. you have to put up pipe hangers anyway you could have put up ser cable and be done with it.
So you mean an expansion coupling such as: https://www.homedepot.com/p/Carlon-...Coupling-Standard-Fitting-E945F-CAR/100124876i would put in 1 inch pvc. and i would also use a extension fitting in the horizontal and vertical runs because it is going to be moving with people walking.
The THWN (wet-rated) I bought is black, red, and green.i posted on another post you have and you need to pull thhn or thwn conductors they have two insulations on them their color and a clear one so it can sit in water it is not going to matter to it.
No, the feed to the subpanel comes through the basement and I used 8-3 NM. So 40 amps it is, I believe.if you are using thhn conductors for the feed in that panel and they are copper and not aluminum and it's considered service boost up the breaker size from 40 to 50 amp. only for service is this allowed and if copper the max ampacity of that wire is 55 amps.
I've had the same experience. What I used wouldn't set. What a pain.I opened up an old tube of v2 recently and it had gotten REALLY weird; turns out there is a hard expiration date.
I was thinking I'd run the PVC conduit (the rigid stuff with the one 90-degree elbow), and pull the wires thru it. I'll pull an extra few feet of wire out the end where the liquid-tight will be, then feed it thru the liquid-tight, and then attach the liquid-tight to the PVC. I guess to attach the liquid-tight, I have to cement a female adapter to the end of the PVC, and then a male fitting on the end of the liquid-tight that screws into the female adapter (unless there's a better way).if you use liquidtite for that length you wil need 3 people the stuff the wires thru. it's round and not straight so will be a BIG pita.
No, I explained it poorly. If I decide to install a 2nd minisplit (a big if), it'll free up a breaker in the main panel (by disconnecting a baseboard unit), and I'll re-route the EVSE wiring straight to the main panel. So the subpanel will either have two minisplits, or one minisplit plus the EVSE.at 40 amps if you put a second ductless on it will seriously be a stretch on the 40 amp main.
Many thanks for bringing this to my attention guys. Looks like I need to allow 2-3" in my 50ft horizontal run (mostly shielded from sun by being under catwalk) and an inch or so on the vertical. But can I not allow for this the way one would for long PEX or PVC plumbing runs, by securing loosely enough that the stuff can just move ? Where the elbow is where the vertical and horizontal runs meet, if I simply don't have a clamp on the horizontal run right AT the elbow, the end of the horizontal can just bend down or up a little (to account for slight shortening or lengthening of the vertical run). Maybe pushing it for the horizontal run, but if it can slide in the clamps, and if it's got that piece of liquid-light (leading up from underneath the catwalk), seems like it could handle that too.Here is your thermal expansion chart
Haha, the wind there is just unbelievable. I'm seriously thinking about putting in a vertical-axis wind generator.it's code to put a expansion fitting on a outdoor pvc pipe run. but keep in mind that the pvc pipe run will move more than usual because of the catwalk. most people don't realize that even a house moves in the wind
I believe it's all plastic. The liquid-tight connectors that kinda screw onto the ends of the liquid-tight. Into PVC female adapters at both ends. One solvent-welded to end of conduit run. Other to reducer bushing, to step size up to 1-1/4", which is what the EVSE needs.fitting wires thru the liquidtite will be hard to do and on the hands. and if you get any metal even on a liquidtite connector or coupling that metal has to be grounded.
thank you. at least someone knows what i mean. the liquidtite is curved so it fightsI once thought it would be easy to "push" three 6awg stranded wires through a 2ft piece of 3/4 liquid tight. Nope.
X2...maybe it's a brand /model thing? Still news to me...never heard of this.
Ah, gotcha.... I've never used much of that...what I did use already had wire pulled in it.I ma not talking about sealtite that has an inner lining. I am t` about flexible metal conduit. (broken link removed). I used a lot of it my boiler controls but short runs. In the case of home run wires for solar from the panel through the house to the basement the wires have to be in metal conduit and flexible metal conduit is the easiest to fish through walls.
I've used an awful lot of MC in barns and attics, but why this stuff, @peakbagger? Was it an application where there was no MC that could work?I ma not talking about sealtite that has an inner lining. I am t` about flexible metal conduit. (broken link removed). I used a lot of it my boiler controls but short runs. In the case of home run wires for solar from the panel through the house to the basement the wires have to be in metal conduit and flexible metal conduit is the easiest to fish through walls.