Glad I found this forum! Sorry for this long post.
I am in the middle of remodeling and have come across some issues with our Heatilator ST36B see through 36 inch wood burning fireplace.
Background. We live just north of Jacksonville, Fl. We have been in the house for 2 years. The home was built in 1992. Neighbors had told me that the fireplace was seldom used. We have used it about a dozen times in 2 years. Fireplace was installed during construction. Much of the interior was completed by the first owner and as I have been remodeling, I have found that he didn’t do many things correctly so I decided to tear out the drywall around the fireplace to inspect.
What I found.
1. There was not a half inch clearance between the firebox and the framing. So I cut the lower framing 2x4’s away from the box.
2. The exhaust duct work is about an inch/ not 2 inches from the framing at the ceiling. (framing is 22 ½ inches vice 23 inches)
3. The holes where the gas lines would go (gas knock out) were plugged with fiberglass insulation that started to char.
4. There is a light switch next to the fireplace that didn’t operate anything (I figured it was for a potential blower/fan) I found the electrical wires (live) on top of the firebox bundled up.
5. Outside air ducting ends at the side of the attic it is not piped for fresh air.
The unit is 15 years old, I am not confident of its integrity and the install. Should I replace the entire thing? We want a see through fireplace and if we replace it, I would like to go bigger (recommendations?)……………… or should I just try and fix everything?
I had a salesperson tell me that blowers/ fans are not worth it and that they seize up and rattle.
Pictures of everything here: http://www.burgett.us/fireplace/index.htm
I am in the middle of remodeling and have come across some issues with our Heatilator ST36B see through 36 inch wood burning fireplace.
Background. We live just north of Jacksonville, Fl. We have been in the house for 2 years. The home was built in 1992. Neighbors had told me that the fireplace was seldom used. We have used it about a dozen times in 2 years. Fireplace was installed during construction. Much of the interior was completed by the first owner and as I have been remodeling, I have found that he didn’t do many things correctly so I decided to tear out the drywall around the fireplace to inspect.
What I found.
1. There was not a half inch clearance between the firebox and the framing. So I cut the lower framing 2x4’s away from the box.
2. The exhaust duct work is about an inch/ not 2 inches from the framing at the ceiling. (framing is 22 ½ inches vice 23 inches)
3. The holes where the gas lines would go (gas knock out) were plugged with fiberglass insulation that started to char.
4. There is a light switch next to the fireplace that didn’t operate anything (I figured it was for a potential blower/fan) I found the electrical wires (live) on top of the firebox bundled up.
5. Outside air ducting ends at the side of the attic it is not piped for fresh air.
The unit is 15 years old, I am not confident of its integrity and the install. Should I replace the entire thing? We want a see through fireplace and if we replace it, I would like to go bigger (recommendations?)……………… or should I just try and fix everything?
I had a salesperson tell me that blowers/ fans are not worth it and that they seize up and rattle.
Pictures of everything here: http://www.burgett.us/fireplace/index.htm