The reason I ask about the isolating the expansion tank is that it was recommended to me, as I’m non pressurized as well.
I thought with posts 149/150 flow estimated to be 9gpm, even at 6.6 a low calculation round trip from the owb through the flat plate and back to the return port of the owb, wouldn’t explain his problem. But what would explain is if there was poor flowthrough the pressurized side of the flat plate, relying on zone flow circs to make that happen.
Can someone steer me in the right direction of what I should be doing plumbing wise on my oil boiler return? It was my understanding on this thread that I should have done exactly what I did but Teeing off the HWBB return and T back into the return on my Oil Boiler.
OWB is up to temp and currently at 200* on display
Inside temp of the actual water ( coming out of the purge valve on both. The supply and the return are both measuring 187* with no load on the indoor system at this time.
I agree with @TCaldwell. The temp probe on the OWB is probably in the water jacket higher than the supply port. It doesn't take much to height to make a difference. I would say you need to try circulating the oil boiler water through the FPHX continuously as long as the OWB is running. Maybe it's just not putting the heat into the boiler often enough because it's only circulating with thermostat call.