I like this puzzle, but I think we could really use 1 detailed schematic to help.
I can't quite tell from the pictures, but I see the oil "return' is tied to the pellet "supply". The pellet "supply" is T-ed to the pellet "return" (is this for return water protection? it looks like there is a valve and it is "off").
It looks like they tried to put the boilers in series on a loop. Kinda primary/secondary style. I see an aquastat on the loop, what does that control?
The more I look at it, the more I think it is plumbed "fine". I think you have a control issue...or you just have a bad component. Are you SURE your circulator pump is good? Since you only notice a problem when it is really cold I get the idea that the zone valves might be opening, but your only flow might be convection.
ac
I can't quite tell from the pictures, but I see the oil "return' is tied to the pellet "supply". The pellet "supply" is T-ed to the pellet "return" (is this for return water protection? it looks like there is a valve and it is "off").
It looks like they tried to put the boilers in series on a loop. Kinda primary/secondary style. I see an aquastat on the loop, what does that control?
The more I look at it, the more I think it is plumbed "fine". I think you have a control issue...or you just have a bad component. Are you SURE your circulator pump is good? Since you only notice a problem when it is really cold I get the idea that the zone valves might be opening, but your only flow might be convection.